I am in the process of renovating a house and intend to re-wire the whole building & install a new consumer unit. Fixed appliances likely to be installed include an electric cooker, boiler, water softener, waste disposal, central heating pump, shower pump, fire alarms, security sensors. There will also be an outside socket in the garden shed.

The house has three floors and an extension. I want to choose a CU that gives me enough MCB/RCBO slots for all the circuits, plus some spare for the future.

I suspect that my two areas of ignorance (below) have been discussed at length on this newsgroup, although I can't find any information at

formatting link
So I wonder if someone could kindly point me to threads or website links that cover the following:

A. The typical electrical circuits to be found in a house (e.g. 2 x ring mains, 2 x lighting, 1 x cooker etc...). I want to find a list of appliances that would have their own circuit protection.

B. The relative merits of RCDs and RCBOs.

Thanks in advance for your assistance.

Reply to
John Aston
Loading thread data ...

Technically, you have a maximum of 100m2 for a ring circuit. However, it is better to anticipate the likely load and use this as maximum. In particular, a well stocked kitchen often has more equipment than should be installed on a single ring main, especially if, like me, you cycle the machines all simultaneously whilst cooking.

As an example, my house has the following circuits installed into a 16 outgoing way Contactum CU. TN-S earthing, 100A DP switch incomer. (60A cutout). RCBOs are double width, as they were the cheapest Type B RCBOs I could find.

  1. B32A/0.03 RCBO. Ring main for entire house except kitchen. (May split into two RCBO circuits in future when loft conversion built).
  2. B32A/0.03 RCBO. Ring main for kitchen. (including 2.2kW dual fuel cooker)
  3. B32A/0.03 RCBO. External electrics (outside socket, outside lighting, future shed supply)
  4. B32A MCB. Radial circuit for kitchen fixed integrated appliances. (dishwasher, washing machine, dryer) remotely switched sockets concealed under worktop.
  5. B16A MCB. Radial circuit for fridge/freezer only. Reduces risk of defrosting, as only a fault on that circuit, or the main service fuse will cut the power.
  6. B16A MCB. Heating system. (Immersion, central heating, heat bank).
  7. B6A MCB. Most of house lighting circuit.
  8. B6A MCB. New lighting circuit (kitchen only currently)
  9. B6A MCB. Alarms (Interlinked smoke/heat detectors + intruder alarm)

If I had an electric hob, there would be a separate B32A MCB circuit for it. When I moved in, the house had 3 operational circuits, a single ring main, a single lighting circuit and a cooker circuit used solely to power the skanky fridge freezer they left behind, as only 2 double sockets were installed in the entire kitchen.

If designing from scratch, rather than upgrading the previously stingy, but safe and well executed system, I would use at least two lighting circuits. It is traditional to do upstairs/downstairs split. However, I would prefer to randomise the circuits, so in the event of the MCB popping, a nearby light will work. It does have the disadvantage that someone might assume the upstairs/downstairs thing and work on a live circuit, though. Quite frankly, if you make assumptions like those, a quick jolt could help you change your attitude!

I would also split the rest of the house ring main into two. However, there is no real reason to change my preexisting circuit. It comes well within the

100m2 requirement. Loading is likely to be very light, with no fixed appliances or heating loads expected. The major requirement is during a gas failure, where I might use up to around 5kW of electric heating. My entire house heating requirement at -3C outside is only 8kW, so it would be difficult to blow the ring using thermostatically controlled heaters anyway.
30mA RCD (whole house) = BAD!!!

30mA RCD (split load) = Much cheaper than RCBOs

30mA RCBO = Much less prone to nuisance tripping. Tripping has fewer consequences. Warm feeling of having done it right.

Obviously, if a TT earthing system, the 100A DP incomer switch should be exchanged for a 100A/100mA time delay RCD. The use of split load RCD/RCBO would remain exactly the same, though. If I had such a system, I would also consider using an RCBO on the kitchen radial, to prevent any earth leakage in the kitchen fixed appliance heating elements taking out my lighting and heating.

As for your list of appliances:

electric cooker = Own dedicated circuit on B32A MCB. Do not install cooker unit with built in socket. They look bad and trail leads over the cooker.

boiler = put on a dedicated central heating circuit MCB (not RCBO). Can share with immersion, especially if sharing controls, such as programmers. All central heating valves, programmers and other controls should be from the same central heating circuit. The CH side (as opposed to the immersion) should be fused down to 3A, either internally in the boiler or in a separate FCU. If there is no immersion on this circuit, use a B3A MCB instead, and a DP switch to isolate the entire circuit next to the boiler.

water softener = 3A FCU off nearby ring main/kitchen fixed appliance radial. Some softeners don't require electrical supply.

waste disposal = 3A FCU (or as advised in installation instructions) off nearby ring main/kitchen fixed appliance radial

central heating pump = off same circuit as boiler. Will be internal to boiler, or connected directly to it in a modern system.

fire alarms = either wire from a regularly used lighting circuit, or give own small radial circuit (i.e. B6A or B3A MCB).

outside socket in the garden shed = separate RCBO circuit only shared with other outside electrics. DO NOT spur from internal socket circuits. DO NOT share the RCD/RCBO with any other circuit or appliances. The outside socket should be off a 13A DP switched FCU rather than directly on the radial. This enables you to turn it off inside, preventing nuisance RCD trips and electricity theft.

Christian.

Reply to
Christian McArdle

Mine's pretty identical to yours. House was originally rewired around 1970, although the original Wylex CU was probably older. Cabling still perfect, but sockets were crap quality and worn out. Completely rewired kitchen and bathroom during refit and brought service and bathroom bonding up to spec and fitted new CU. Most of the ground floor lighting has been rewired as a side effect of bringing it under home automation control.

These two I have on one circuit, but not RCD protected.

I would suggest using C6A for lighting circuits. It may reduce the chance of a filament lamp tripping the MCB. BS1361 cartridge fuse is another option (probably a better option).

I put the circuit in although I don't ever intend having an electric hob myself. For now, it has an unswitched 13A socket on the end with the gas hob spark generator plugged into it, and a 45A cooker switch ;-)

Strangely, the 1970 rewire did install two ring circuits, but they were joined into one big ring in the CU, which also makes me think the CU was older and not changed at that time.

and doesn't conform to the regs

One disadvantage of most RCBO's is they give no clue what tripped them, earth leakage or current draw. There were some types where the dolly only moved halfway to the off position when the RCD part caused the trip, but I haven't seen them for a long time now.

...and the cooker doesn't want RCD protection, but all the worktop sockets do, which is incompatible with a combined socket.

Moreover, all the central heating controls should all be switched off by the one boiler isolation switch.

There are some rules (which I don't remember, and didn't seem very sensible to me) about sharing smoke detectors with lighting circuits, and relate to the type of battery backup the smoke detectors have. In my case, the smoke detectors run off the alarm anyway, and use the alarm battery in the event of a mains failure.

Reply to
Andrew Gabriel

I'm not worried. I do not possess a filament light bulb in the house, except in my Maglite. I prefer MCBs to fuses whenever possible, as it is easier to reset at 2am, especially when you've got no spares.

Mine is similar, but not quite. The ring went down from the old CU, round the ground floor and then up, past the CU to the upstairs and back down again. I can split it simply by cutting the cable and crimping an extension. I'm just too tight to buy another RCBO until I have to!

Christian.

Reply to
Christian McArdle

Thanks for such a comprehensive reply.

Based on your excellent response and a bit of background reading, I have pencilled in the following circuits (and protection) for my house:

Ring Main A ...32A RCBO G/F Kitchen (incl. fridge/freezer)

Ring Main B ...32A RCBO G/F Dining Room, Lounge, Hall

Ring Main C ...32A RCBO

1/F Bedrooms, Bathroom, Landing

Ring Main D ...32A RCBO Extension: Playroom, Utilities (washer/dryer), Study

Radial A ...6A MCB Lights on east side of house

Radial B ...6A MCB Lights on west side of house

Radial C ...6A MCB Lights in extension

Radial D ...32A MCB Cooker

Radial E ...16A RCBO Immersion Heater/boiler controls/pumps

Radial F ...6A MCB Fire/Security alarms

Radial G ...20A RCBO Garden sockets & lights

Assuming that the RCBOs are double width, I guess that I need at least a

17-way consumer unit. Did you put your RCBOs side-by-side? I read somewhere on this NG that a RCBO can "trip" an adjacent RCBO.

The garden lights must be switched on/off from the house. The shed sockets/lights must be switched on/off in the shed. Is it still OK to run the whole lot off one circuit ("Radial G", above)?

My earthing system is TN-S. I guess you'd advise that I would be better served by a switch than a 100A/100mA time delay RCD at the incomer.

My thanks again for your help.

Reply to
John Aston

Absolutely do not put your fridge/freezer on an RCBO circuit, unless you like coming home from holiday to a rotting stinking mess. It is better to put it on its own circuit, or at least shared on another MCB only circuit. You can always cut out one of your lighting circuits to make room.

OK.

OK.

OK. Although containing high current devices, having just a washing and a dryer on the circuit shouldn't cause any overload.

Might be overkill, could probably combined with another lighting circuit.

OK.

Use an MCB, rather than an RCBO. Although an RCBO is less prone to nuisance trips than a shared RCD, there's still a chance of a spurious pop when you are on your winter skiing break, leading to your house freezing, possibly causing damage.

OK.

You can put them side by side, no problem. When populating the consumer unit, it is best to order as reducing ratings, starting with the heaviest circuits next to the incomer. Remember that with an RCBO installation, you want a "standard" isolator incomer (except for TT), rather than a fancy split load unit.

Absolutely. Consider having a DP switch (or even FCU) on the run to the shed. Then you can ensure that everything is turned off without having to brave the weather.

So, with these modifications, you get:

  1. B32A RCBO - Kitchen ring
  2. B32A RCBO - Reception ring
  3. B32A RCBO - Upstairs ring
  4. B32A RCBO - Extension/utility ring
  5. B32A MCB - Cooker
  6. B20A RCBO - Outside
  7. B16A MCB - Heating
  8. B16A MCB - Fridge/Freezer
  9. B6A MCB - Lighting A
  10. B6A MCB - Lighting B
  11. B6A MCB - Alarm

I make this 16 outgoing ways using double width RCBOs, or 11 outgoing ways using single width RCBOs. You've probably got some overkill on the ring mains and could combine some, too. For example, you might swap the Utility RCBO for a 32A MCB for just the appliances and use the Reception ring RCBO to cover the sockets in the extension. This would save you an RCBO (and give you an extra way if using double width units). It also removes likely earth leakage culprits (i.e. the washing machine and tumbler) from the general purpose ring main.

Christian.

Reply to
Christian McArdle

You can get single width ones, although it may depend on the make of CU.

Check the manufacturer's spec. It varies, and isn't just related to RCBO side-by-side -- in one case they can't be used with MCB of 40A or more side-by-side IIRC.

Reply to
Andrew Gabriel

"Andrew Gabriel" wrote | > fire alarms = either wire from a regularly used lighting circuit, | > or give own small radial circuit (i.e. B6A or B3A MCB). | There are some rules (which I don't remember, and didn't seem very | sensible to me) about sharing smoke detectors with lighting circuits, | and relate to the type of battery backup the smoke detectors have. | In my case, the smoke detectors run off the alarm anyway, and use | the alarm battery in the event of a mains failure.

IIRC if you use a lighting circuit (where you will probably notice a failure fairly quickly) you have to have battery[1]-back-up smoke detectors, and if you use a dedicated circuit (which would go faulty for weeks without being noticed) you don't have to have battery-back-up.

Owain

[1] Although some have a whopping big capacitor these days, I think
Reply to
Owain

Yes, that sounds familiar now you mention it ;-)

Reply to
Andrew Gabriel

Some single width RCBOs are single pole only. Would you recommend a RCBO that disconnects the neutral as well?

Reply to
John Aston

there is no requirement a standard CU has hard wired neutrals

Reply to
Chris Oates

Could you use a single pole RCBO though to protect an outdoor circuit (or any internal socket close to the back door to the garden)?

Looking though the catalogues, there is a much wider range of single pole (solid neutral) RCBOs than there is for double pole RCBOs.

Reply to
John Aston

A DP is nice, as it can act as an isolator for the circuit. Particularly useful for maintainance, or if a neutral-earth short has caused the trip on that circuit (will prevent other RCBOs tripping too). However, there is no requirement, AIUI. After all, an MCB is single pole.

Christian.

Reply to
Christian McArdle

I guess, though, that I couldn't use a single pole RCBO though to protect the circuit for the garden shed. I'll probably protect this circuit with a MCB at the consumer unit and a RCD externally.

Reply to
John Aston

I'd agree with that, nearly! A fault on one circuit wouldn't affect other RCBO's unless they were upstream. If there is no upstream RCD then SP would suffice but if there is then I would use DP.

SJW A.C.S. Ltd.

Reply to
Lurch

No, it could affect an RCBO at the same level.

Consider two SP RCBO circuits in a CU, called A and B.

There is a neutral-earth short on circuit A.

A high current device on A draws some current. A small proportion of the return current from this goes through the earth fault rather than the neutral, tripping the RCBO. All well and good, exactly what you want.

However, now a device on circuit B draws some current. As RCBO A has only cut the live, the neutral current from B could go into the A circuit neutral and through the same neutral-earth short, causing B to trip also, even though the earth fault is on a different circuit.

Had A been fitted with a DP RCBO, this neutral would have been cut, so B wouldn't trip. It is possible that B would trip first whilst A is still operating. However, once A had tripped or been manually pulled, B would not repeat the experience.

Christian.

Reply to
Christian McArdle

Indeed. I've already said 40 Hail Marys.

Christian.

Reply to
Christian McArdle

easy way to do this if short of space is to run the circuit through ab RCD switch as found in consumer units but mounted in a 2 width box like this

formatting link

Reply to
Chris Oates

I'll let you off, we all have bad days. I'm having one today actually! Could be a bad year though, the bad days seem to have merged since 1st Jan!!

SJW A.C.S. Ltd.

Reply to
Lurch

Hager do single module RCBO's in a double pole flavour. Cant remember what the numbers were off the top off my head, I'm thinking AD010B but don't rely on that as correct! Bear in mind you want some spare capacity, around 20-30% I usaually allow. If you were to use Hager then a 14 way board would be ample.

SJW A.C.S. Ltd.

Reply to
Lurch

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.