formatting link
>

At 10x rated current a type C can trip in as little as 0.0015 seconds. I doubt it would do. A wire fuse is closer to a D type, which is orders of magnitude slower at 10x rated current.

NT

Reply to
meow2222
Loading thread data ...

Sounds like an urban myth. Switching of E7 and similar loads is controlled by a phase modulation of 198KHz radio 4. If you have a big radio, try tuning into R4 with the BFO switched on...

James

Reply to
James Salisbury

/Some/ E7 is teleswitched. A lot isn't. timeswitches are still widely used. Some suppliers offer industrial tarrifs of variable hours which are teleswitched. You (and the supplier) get what is paid for.

Reply to
<me9

snipped-for-privacy@care2.com coughed up some electrons that declared:

I don't have my books to hand, so I'll not argue. But if that is correct, then the conditions for putting in a Type D breaker or something with a similar trip curve are considerably more onerous in terms of having a low loop impedance on the local circuit *and* on the supply (ie in the event of a dead short L-E fault, would the breaker or fuse clear before the cable damages itself through overheating?).

It would be quite possible to have a perfectly ordinary and good installation where adding a type D to a random circuit would make it both non compliant and dangerous (particularly from risk of fire, but also shock if the breaker/fuse cannot reliably clear a fault.

However, this does change if there is RCD protection (don't think that was mentioned) - but even so, personally, I would want to then ensure that a L-N fault would clear in the expected times, which is an easier target to meet, but not necessarily a forgon conclusion.

I'd be cautious about jumping straight to something with that sort of characteristic without risking a few quid on the middle option first (there's always ebay if a Type C doesn't work out).

IIRC (memory poor, open to correction) a Type C is several times less sensitive on the instantaneous trip part of the curve compared to a Type B, so there's a good chance it would buy enough margin.

I'm happy to come back tomorrow and reel off some numbers, or I think if one digs into Hager's literature, the trip curves for most of their devices are in there somewhere. Might have a rummage later...

Cheers

Tim

Reply to
Tim S

You put the dimmer after the switches and leave it on full. A soft start dimmer will just limit the current when you switch on and do sod all once on.

Reply to
dennis

10x rated i is a reasonable ballpark for a toroidal startup surge. That's 12.5A in this case, which is only just over 2x the MCB's rated i - I was thinking 10x MCB rated i, so you may well be right with a type C.

NT

Reply to
meow2222

snipped-for-privacy@care2.com coughed up some electrons that declared:

Aye - I was more concerned about randoming banging Type D's - or something equally thick skinned - in without a more detailed test of the installation (loop impedances mainly), which is why I was discouraging it.

Reply to
Tim S

There are dimmers with two way switches - so assuming you leave it full up should be ok. But I'm not even going to suggest this to them.