>> I duly ordered one (Hager) from TLC - they list them but the branch
>> doesn't stock them. After two weeks of phoning and it hadn't came in I >> got
>> one elsewhere. And went to fit it today. Only to discover the lighting >> MCB
>> was a 10 amp one, and I'd got a 6 amp. I suppose I should have checked -
>> but the CU is so high it requires steps to read that sort of thing. >>
>> But I'm slightly concerned about just fitting a 10 amp C type. The wiring
>> is original so about 25 years old. It's a small two bedroomed town house
>> with only one lighting circuit. But lots of low voltage lighting. The
>> lighting wiring is definitely 1mm at the CU. The house is timber framed
>> with brick cladding, and well insulated. The CU is pretty new and 17th >> edition. >
> Well 1mm is good for 16A if not in insulation etc. So that may still be
> ok. Have you counted up the total actual load? Could it be that the
> nominal load is actually under 6A and the installer was just trying to
> cure surge problems by over speccing the MCB?
>
> (note also on a 10A circuit some smaller lamp fittings like SES, will be
> inadequately protected)
>
All light fittings I've seen are rated at 6A. I therefore thought the MCB rating should match this, but am I wrong here?
After all the rating of fitting would be associated with the load and not fault current?