I found a property with Gas Hob and connected with flexi and flexible hose is connected like as '0'shape is it acceptable ?
is flexible hose connection is acceptable with Gas Hob if yes when ?
Feb 26, 2019
Last reply: 7 years ago
3 Replies
Follow replies to this discussion?
First reply
I think its OK for existing installations, but not for new ones. I'm not Gas safe though.
Read the full replyInformation here may be outdated?
AIUI, it's only acceptable if the hob manufacturer says so ...
I think its OK for existing installations, but not for new ones. I'm not Gas safe though.
The word "11.1.3 A gas hob shall be connected to the termination point by means of rigid pipework or, unless stated otherwise in the manufacturer?s instructions, a flexible connector and self-sealing plug device conforming to BS 669-1"
Note there was an old version that prohibited flexible piping.