Help I am totally confused and do not know what to do



Ed Sirret says the following on 2004-10-14



In the Gas Fitting FAQ below you will still that the use of a flexible hose is deprecated (and almost impossible to install in a compliant manner for the supply of an inset hob). As of 20th November the loop hole which permitted the use of flexibles is closed with a revision to BS 6172.



I have just purchased a gas hob (inset into worktop) from B and Q Sterling BGH1



the installation instructions state



Natural Gas the appliance is designed for UK installation using a flexible connection with tubing in accordance with the regulations inforce length of 900mm is recommended.



Sterling customer services tell me the following they have never heard of this. The hob only started to be sold at the end of last year The print date on the instructions is 11-10-2004



What do I do? Which is the correct way of fitting this? Are there any insurance implecations of fitting not in accordance with manufacturers design What would a Ed do? What would any other corgi Fitter do? Does anyone have the exact text for BS 6172:2004 as I cannot find it Who do I alert if Sterling are wrong? Where are you based Ed? email to phil AT nimbusweb DOT co DOT uk please regards Phil


Don't you just hate it when that happens?

The confusion doesn't surprise me in the least. I'm have no doubt that Ed's FAQ is correct, but if you want reassurance why not just phone CORGI direct? See

formatting link
(although having said that, last time I phoned CORGI about a regs query, I got a different answer each time I phoned them!)

Available in libraries, but you won't find it online without paying 60 quid(?) for a pdf file from the BS website - something which never fails to irritate me. Why should we be told by the Powers That Be that to do some task legally we have to comply with BSxxxx, but then we can't find out what BSxxxx actually says?!

David

Never mind all that, if you ever intend using and sleeping in this house which of the two fitting alternatives seem safest. ?

-- Mark§

This does seem anomalous - the regulations in force being that you should not use a flexible gas hose for a fixed inset hob!

However the general requirements for the installation of an appliance supplied by a hose would still apply - and I say in the FAQ they are quite restrictive: Not going to be disturbed. Not in contact with anything that might become over 70C Hanging in a neat unstrained U shape.

What I would do depends if the instruction explicitly forbid the use of rigid pipework - then I would ask the manufacturers for clarification. Perhaps the hob is designed to be easily removed from the worktop? Why?

Further to my earlier post on the above, I just came across an

*unsubstantiated* quote from the trade rag "Gas Installer" stating that a hob connection has to be rigid *unless otherwise stated by the appliance manufacturers*!

Ed, or somebody else who has access to back issues of Gas Installer, could you confirm this? Isn't mentioned in the FAQ... if it's true, it strikes me as a total joke, because in the OP's scenario it means that a flexible hose must be used, notwithstanding the fact that the manufacturer is apparently unaware of the change in regs which states that a rigid connection must be used...!!

David

Does it specifically state (or imply) that a rigid connection is prohibited?

As per the manufacturer's instructions

Scratch head, mutter incantations in gasinstallerese, burn incense^H^H^H^H^Hsmoke pellet, ask corgi tech info line 3 times and take majority opinion :-)

11.1 General ... 11.1.3 Unless stated otherwise in the manufacturer's instructions, a gas hob shall be connected to the termination point by a rigid fixed connection. ... 11.1.5 Any flexible connector shall not be subjected to direct exposure to hot flue products or to contact with hot surfaces (see also 11.4). 11.1.6 Where rigid pipework is used, an isolation valve with means of disconnection shall be provided. 11.2 Connections for 2nd family gases 11.2.1 The gas installation pipe to the termination point shall conform to BS 6891 or IGE/UP/2 [17], as appropriate. 11.2.2 Any flexible connector shall conform to BS 669-1 or BS 669-2, as applicable. COMMENTARY AND RECOMMENDATIONS ON 11.2.2 The flexible connector should be installed such that it cannot be subjected to undue forces either in anticipated normal use or whilst being connected or disconnected. The flexible connector should be positioned in such a way that it will not suffer mechanical damage by being trapped by a stability device (see Clause 12). 11.2.3 The location of the termination point shall be in accordance with the cooking appliance manufacturer s instructions, where this is specified. COMMENTARY AND RECOMMENDATIONS ON 11.2.3 The termination point should be permanently attached to a firmly fixed gas installation pipe and positioned such that the flexible connector hose hangs freely downwards. The termination point should be securely fixed to the wall by means of a backplate adaptor or suitable alternative. The termination point should be securely fixed to the wall immediately behind the appliance at a height of approximately 750 mm from the floor, unless otherwise specified by the manufacturer. The termination point should be accessible for disconnection after moving the cooking appliance.

Ah - that substantiates the 'unsubstantiated' quote in my previous post to this thread. So give that in the OP's case, the mfr has never even heard of the 'rigid connection' regs, it is barmy that the mfr's instructions take precedence. (Isn't it?)

David

AIUI the manufacturers instructions 'trump' the regs. I suppose this is to allow for an appliance which out-performs the rest of the field in some respect [1]. However in the case of this inset hob we seem to have the opposite case where the manufacturers require the installation to be less than best practice. Crazy.

[1] For instance the clearances to most modern boilers casings from combustible materials are substantially less than the 75mm (IIRC) required in the regs.