Been chasing a weird one at the park I maintain. Guests keep complaining their ACs cutting out and microwaves running hot, so I started metering the pedestals. On one of the 50 amp sites I'm getting about 130 volts from one leg to neutral and only 90 from the other. Total across the two legs reads right around 240, which makes no sense to me.
When I opened the pedestal up to check the lugs, the wiring in there is a mess. Multiple conductors crammed under single set screws, some taped-up splices jammed off to the side, dirt and cobwebs everywhere. Looks like it's been patched a few times over the years and never cleaned up. Not my work, for the record, but I'll be redoing it when I swap the pedestal out. My guess is a loose or corroded neutral somewhere, since the two legs seem to be swinging away from each other instead of both drifting low. Does that sound right? And if the neutral is suspect, should I be looking back at the main panel feed too, or is it usually just the connections at the pedestal itself? I metered a couple neighboring sites and they seem fine, so I'm hoping it's contained to this one box.