I am installing a new built-in oven and hit the usual problem of the horrible connectors they always seem to come with. However this one seems even worse than usual and I'm a bit stumped as to how to do a proper job of connecting it.
I have a dedicated 32 amp MCB for the oven and (electric, induction) hob and it has a 6sq mm cable running to the kitchen units.
However there is absolutely no way that one can connect 6sq mm cable to the oven. The connection block is too small. The only cable that I think I can reasonably connect to it is 2.5sq mm because the screw terminals are such that only single, solid wire can be reliably connected to it.
There's not enough room for any sort of termination on the cable. I've tried and I have a wide variety of crimps in many shapes and sizes, while you can terminate a cable with a 'ring' that will fit under the screw the body of the crimp is too fat to fit through the slot provided for the cable.
The oven is rated 2.3kw so 2.5sq mm is perfectly adequate, the problem is that it's not ideal for allowing the oven to be slid in and out and it's not properly protected by the 32amp MCB.
What options do I have? I suppose I could have a local FCU for the oven but it seems a bit overly complex and discrimination might be a problem. I can't see *any* way to connect flexible cable to the oven so I think it's stuck with at least a short length of 2.5sq mm. The best I can do at present is to take the short length of 2.5sq mm to a junction box (or terminal block) on the back of the oven and run a more flexible cable from there. Can one get high temperature 2.5sq mm cable with solid conductors that I could rate at 32 amps? That would be be the neatest solution I guess.
Or maybe I should take the back off the oven and replace their crap connector!