I have to fit a room thermostat into a building where there is already an old three-wire connection for a (mechanical) thermostat, but no existing thermostat. So it is not immediately obvious which wire is which.
There is no earth connection. Using a multimeter, what is the simplest and safest way of identifying each wire?
With all the electricy off at the MCBs, but on at the main switch, find which wire is less than a couple of ohms to neutral in any handy socket. (Possibly one of the others will only be few tens or hundreds of ohms if there is something inductive connected, but ignore this.) That wire is probably neutral. With the electricity on check which wire is live. That is the live wire. The third wire is switched live.
Alternatively, look at the other end and note the colour code.
Live is easy to identify, it's 240v to the nearest earth. Neutral & switched live: with power off N has near zero resistance to neutral, swL will have much more R.
Thanks to you and Roger. One of the problems is that there *is* no handy socket nearby to which I can measure the voltage/resistance to earth and live; but no doubt I can get round that.
socket, metal light fitting, radiator, water tap or drain, most of those ar e earthed, but not all. The other option to identify live is to measure the 3 voltages between the 3 wires, live to N and live to swL will both give 2
40v, N to swL should give 0v. (Y plans do complicate this.)
Live to swL can give you Ov either because it is open circuit or because (as you say) some other control has connected ti to live. If N to L and N to swL are both 240v then further measures are necessary. Probably, as you say, something to do with motorised valves and their switches.
If N to swL is Ov, which is which, if live to either gives 240V? I think your scheme only works if you know exactly what is connected at the other end and even then ambiguities are left.
Another possibility if you use a high impedance meter and swL is open circuit is that N to swL will give you 5 or 10V AC. What do you conclude from this?
No doubt, but lots of appliances are supplied without an earth. I was rather horrified the other day to find that my 3kW convection heater (the kind you mount on the wall) had no earth wire, even though it's made entirely of metal. It's one of the leading brands.
It's a Honeywell and the wiring diagram essentially the same as the one ARW has just posted, but without the earth. It has an unused pin 5 so I guess one could that for the earth.
I'm not sure what ARW means by me misunderstanding the diagram. The connection to pin 3 is clearly a switched neutral (switched through the load). There is no switched live feed to the thermostat.
I agree the diagram looks grossly misleading. But we must assume that the wire marked 'live' is indeed a direct connection to live. The yellow wire to terminal three does not connect to anything else in the thermostat box (although terminal three also connects to one end of the heater in the thermostat which heats the bimetal strip and is used to reduce hysteriesis), but wanders off down the cable to the boiler controls, described hear as 'heating system'. When the thermostat is demanding heat the switch from terminal one connects to the contact on terminal three and supplies live voltage to the boiler control. The boiler control certainly will have its own neutral, but this is connected directly at the boiler end and does not rely on the neutral wire in the thermostat. Although electrically the boiler control neutral is connected to the terminal two neutral at the boiler end, there is no wire doing this connecting in the thermostat box despite the junction shown, and just one neutral wire comes to the thermostat purely for the purpose of supplying a current return for the anti-hysteresis heater (called anticipator in the diagram).
If you imagine the orange 'heating system' box dragged off the page, still connnected to its blue and yellow wires, and down the corridor and connected by a yellow blue and red ( and also earth!) cable to the thermostat then things fall into place. In theory the red and earth cable do not need to come from the boiler control, as they are just live and earth, but in practice this is the correct way to wire it. The live incoming to the thermostat is connected to the switched live yellow wire and activates the boiler control.