Re: cable width for wiring thermostat

My Dad is installing a Danfoss RMT 240 volt room thermostat to control

> a Danfoss HS3-3 point mid-position motorized valve. Would 3 core and > earth 1mm cable have sufficient current carrying capacity for this > application? > > Thank you for your help.

Well as 1mm 3 core and earth is rated at 12 amps I would say yes.

Trevor Smith

Reply to
Trevor Smith
Loading thread data ...

Yup, it'll be more than enough. It's physical robustness is more significant than its current-carrying capacity in this context.

Rick

Reply to
Richard Sterry

Yes, but don't lose sight of the fact that - in a Y-plan system - the 3-port valve switches the boiler and pump on in some modes, and the current for that *also* goes through the room stat - so it's not *just* switching the valve.

Even so, 1mm cable should be ok.

Reply to
Set Square

We're still talking small currents. A 5 amp fuse is fine for most systems.

Reply to
Dave Plowman (News)