Re: cable width for wiring thermostat

Aug 05, 2004 3 Replies


My Dad is installing a Danfoss RMT 240 volt room thermostat to control


> a Danfoss HS3-3 point mid-position motorized valve. Would 3 core and
> earth 1mm cable have sufficient current carrying capacity for this > application? >
> Thank you for your help.

Well as 1mm 3 core and earth is rated at 12 amps I would say yes.


Trevor Smith



Yup, it'll be more than enough. It's physical robustness is more significant than its current-carrying capacity in this context.

Rick

Yes, but don't lose sight of the fact that - in a Y-plan system - the 3-port valve switches the boiler and pump on in some modes, and the current for that *also* goes through the room stat - so it's not *just* switching the valve.

Even so, 1mm cable should be ok.

We're still talking small currents. A 5 amp fuse is fine for most systems.