10 amp fuses - quick moan

Ah, thank you Adam, that is probably why there are none in this part of the world

Reply to
The Natural Philosopher
Loading thread data ...

In Britain we say 'metricated'

Reply to
The Natural Philosopher

Every half hour? Here we have one bus a day!

Reply to
The Natural Philosopher

The MCB. should trip at around 10-20A

Reply to
The Natural Philosopher

Wish I could do that with my students ;-)

Reply to
whisky-dave

Size of the metal blown out between the blades of the snips?

Reply to
Adrian Caspersz

A common misconception it seems :-)

MCBs do not limit current. They trip in a time inversely proportional to the overcurrent. In the time before they trip, the magnitude of that overcurrent is limited only by the fault loop impedance.

So a 6A MCB will typically carry 10A for about 10 mins. 20A should trip it in no more than about 30 secs. 30A should be enough to trip it on the magnetic part of the trip curve in 0.1 secs.

The fault current on the cable and snips would (in this house at least (ELI/Ze 0.24 ohms) would be around 200 - 900A depending on how far you are from the CU. I suspect in Adam's place, he will be needing a new set of snips!

Reply to
John Rumm

I bet you live somewhere nice though.

Chavvy areas usually have better bus services. Bus every half hour to Aldi and the VD clinic here.

Owain

Reply to
Owain Lastname

Owain - offer is still open if you want a few 10 amp fuses.

Just resolve scott(dot)simpson[at]gefion(dot)myzen(dot)co(dot)uk

Reply to
Scott

Every 8-12 mins where I live oh so what does that say about my area ;-)

and we did have 2 BMWs broken into one the steerring wheel was stolen and the other a disabled badge was stolen.

Reply to
whisky-dave

I've got loadsa 1 1/4" fuses of all sorts, Quick blow, (I bet you know a few 'ladies that offer that) . anti-surge etc...

Reply to
whisky-dave

At one time it was common to find light duty flex used.

But since most can only ever buy/find 13 amp fuses think the regs were changed so all flex should be capable of taking that out in event of a short.

Reply to
Dave Plowman (News

No buses here.

Bill

Reply to
williamwright

I thought the new regs were 3A or 13A and that's it. Our new FGs came with a IEC lead/cable which has 3x0.75mm embosed on it , the plug has a 13 amp fuse and the IEC connector is rated at 10 Amps. I'd had thought a 3Amp would be fine for the FG but guessing the fuse is for the 'lead/cable' I think the FG has an internal 2amp fuse. Almost everything we buy uses a IEC lead with a 13amp fuse.

Reply to
whisky-dave

It'd probably work for some of them - if you were allowed to.

Reply to
SteveW

Well explained.

Reply to
ARW

No mention of needing clean underwear though… ;-)

Tim

Reply to
Tim+

I'm sure I've seen a few (this century) with 5A or 10A fuses (or perhaps they've been a junk box since the last century) !?

Reply to
Mark Carver

Many of the "Cold" IEC leads are only rated to a maximum of 10A. Some of the dodgier ones, even less.

Reply to
SteveW

Thank you, but I've passed it back to its owner.

Even with a 13A fuse it's safer than the guy's microwave oven transformer in a lidless storage box used for fractal burning.