if I am low on freon will this caus my central ac to trip the breaker

Jun 03, 2012 2 Replies
Saved reading
Jump to replies (2)
 Low refrigerant may cause the breaker to trip when the compressor has been running for a while, not immediately on startup. It happens because the flow of refrigerant also cools the compressor and its motor and if there isn't enough of refrigerant, the motor overheats and draws more electrical current, and that's what trips the breaker. If it's been idle for awhile and you are just turning it on, the lack of refrigerant would not yet play a role. 

Does any part of the system come on when there's a call for cooling? Do you hear any noises at all when you just turn A/C on? When you say that A/C would not turn on when you reset the breaker, do you have to wait a certain amount of time until it does or has it just stopped working for good? 

The proper refrigerant charge is important to normal operation of the A/C and you'll have to address the issue of low refrigerant at some point, but to fix the issue at hand I think you should be looking for an electrical culprit: a bad breaker, contactor, bad compressor or condenser fan motor capacitors, bad wiring.

Troubleshooting these parts requires you to work with high power high voltage electrical equipment and if you are not completely comfortable with and knowledgeable about this equipment and lack proper tools, it is imperative for your safety to  call a professional HVAC technician.

every time I turn on my central ac the breaker trips. if I reset the breaker the ac will not turn on


Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required