I actually see two potential issues here. When you say "two breaker switches", do you mean two separate single-unit breaker switches? Or do you count a double-slot two-pole switch with a handle tie between the two switches as one unit and call it "one switch"? Either way, it is…

Read the full reply

I actually see two potential issues here. When you say "two breaker switches", do you mean two separate single-unit breaker switches?  Or do you count a double-slot two-pole switch with a handle tie between the two switches as one unit and call it "one switch"? Either way, it is either rather unusual or simply wrong setup. The electrical furnace is a very high power appliance (8-10kW at the minimum) and it should be on a 3-wire 120/240 volts single-phase service which has two live wires to increase its current capacity. So the double pole breaker is designed to trip and disconnect both live wires in the event of over-current on either one of them.

The furnace is internally wired to use the current from both live wires and would sort of limp along at about 1/4 of its capacity if one of the live wires is disconnected. The blower in the air handler that is pushing both hot and cold air through is most likely connected to the breaker of the outside A/C unit (yet another two pole breaker you would normally see in the panel) and that's why the A/C keeps working.

Anyway, I just wanted to point out that if you have two breakers labeled "Furnace", you have to have them as a single action two-pole breaker with a common trip. Otherwise you may disconnect only one of the live wires feeding the heating element and it will still be energized through the other one and someone can get hurt.

Oh, and the other potential issue I was talking about is that the furnace was not properly wired from the beginning and was probably constantly consuming the 2kW during its entire lifetime. I would need to know more about the furnace (model #, approx. year) and your confirmation about the circuit breaker type to dig deeper into this. But in the end it may require a repair that's best left to a professional HVAC technician anyway.

Be careful and stay safe while you're looking into this electrical issue.

Thanks for stopping by our site!

My electricity usage was way out of line for the size of my home. I received a monitor from my electric company that shows the kWh being used throughout the day. There was a consistent 2kWh usage from somewhere. I turned off the breaker switches one by one to narrow down where that 2kWh usage was coming from. What I found was that there are 2 breaker switches labeled FURN for the electric furnace. It was one of those switches that when turned on was using 2kWh. Keeping that switch turned off, I turned the A/C back on and it works. Does anyone know what that other switch is for and why it would be using so much electricity if the furnace was not turned on? Is it OK to leave that breaker switch off?


If the furnace blower runs continuously, the limit switch, designed to shut off the furnace when the plenum gets too hot, might need adjustment. The limit switch should have a lower pointer set at 90 degrees Fahrenheit and a higher pointer set at 115 degrees Fahrenheit.