Wiring help for Centaurstat 7

I wish to replace a Satchwell TLM2253 with a Horstmann Centaurstat 7 for a conventional CH system (fully pumped with programmer and 3-port valve). The existing Satchwell stat (2253) has three wires cabled up to terminals #1, 3 and #4. Reading its installation manual, #1 and #4 are Neutral while Live is #3. I gather #4 is for a shunt accelerator heater because the 2253 uses a bi-metallic strip mechanism ?

How do these map to the Centaurstat terminal block ? Am I correct in thinking I need only cable up to #1 (Live) and #2 (Neutral) ?

Thanks Paul

Reply to
Paul G
Loading thread data ...

Your existing stat probably has live, switched live, and neutral. The neutral is indeed to allow the shunt resistor to be powered.

The new stat will not require a neutral at all (you can park it on terminal 4 of the centaurstat). It just needs live and the switched live connected to terminals 1 and 2.

Reply to
John Rumm

The Centaurstat doesn't need a neutral - tape it up. It needs the live feed and the switched wire that goes to the boiler. I think your reading of the Satchwell wiring is a bit incorrect.