I think this is my first biggish question to the group! Having read similar threads so far I don't think the following has really been covered.
Introduction
------------ At my mum's house we currently have a Off Peak supply which was being used for water heating, washing machine, dish washer and tumble dryer. The new heating system will be taking over the hot water duties. Thus we are planning to discontinue the off peak tariff.
We have a TT installation with our own earth rod and over head supply.
Current
------- The current consumer unit is a surface mounted 16 way insulated MK sentry "s" series (the range before the current with the smoked gray transparent lid). It's configured as a multi-incomer with the "mains" and off peak supplies as below
way(s) 1 - 2 80A 30ms RCD "Mains" incomer way(s) 3 32a MCB Cooker way(s) 4 16a MCB Central Heating way(s) 5 32a MCB Ring Main 1 way(s) 6 32a MCB Ring Main 2 way(s) 7 16a MCB Outside Sockets way(s) 8 6a MCB Lighting 1 way(s) 9 6a MCB Lighting 2 way(s) 10 blank way(s) 11 blank way(s) 12 - 13 80A 30ms RCD "Mains" incomer way(s) 14 32a MCB Washing Machine and Dishwasher radials way(s) 15 16a MCB Tumble Dryer Radial way(s) 16 16a MCB Immersion Heater Radial
(you now know what components we've got).
Proposed
--------- As I mentioned we would like to remove the off peak tarrif and change the system into a split load configuration. So far I've come up with the following configuration (which will involve a bit of re-wiring in the house).
way(s) 1 - 2 100A Switch "Mains" incomer way(s) 3 - 4 80A 30ms RCD Split One way(s) 5 32a MCB Cooker radial way(s) 6 16a MCB Central Heating radial way(s) 7 16a MCB Fridge & Freezer radials way(s) 8 6a MCB Lighting 1 radial way(s) 9 6a MCB Lighting 2 radial way(s) 10 - 11 80A 30ms RCD Split Two way(s) 12 32a MCB Ring Circuit 1 way(s) 13 32a MCB Ring Circuit 2 way(s) 14 32a MCB Ring Circuit 3 way(s) 15 16a MCB Outdoor Sockets radials way(s) 16 16a MCB Immersion heater radial
Comments
--------
- Each RCD will be fed via the one Switch disconnecter (live and neutral). This in turn will be fed from the Boards meter.
- Since we already have the 2 RCD's it's cheaper to buy a switch disconnecter than a time delay RCD and cascade the "split two" circuits as per conventional set ups.
- TT set ups require everything to be protected via a RCD
- The clear advantage is that all circuits are protected via a 80A 30ms RCD (as they are at the minute with no trouble trips yet - just a duff Iron), instead of a slower 100ms Time delay RCD.
- Where Ring Circuit 3 (could/would) be a new ring formed around the utility and adjoining garage. This would include the Washing Machine, Dishwasher, Tumble dryer sockets (see below).
Queries
-------
1) Does this sounds like a good plan or is there any concerns or suggestions for improvements?
2) The incoming Switch disconnecter will need to have a connection to the two downstream RCDs for the live and neutral connections. Is it permissible (or even possible) to connect two 16mm sq tails into the cage connectors on the switch (50mm sq capacity)?
- For the short distance between the Switch to the RCD could 10mm sq tails be used (pretty sure the answer is no here!)
- Some form of crimped furrels
- external henly blocks - ugly
- would getting an extra MK split load kit be advisable and use the extra cables (these have crimped ends and are much more flexible)
3) The above mentioned white goods (Washing machine, Dishwasher and Tumble drier) are currently connected with standard single 13a sockets and all wired back to the CU with 2.5 mm sq T+E. But into a 16a and 32a MCB. To save hassle could these remain as radial circuits back to a single
32a MCB (The total loading on these would be more than 32a, if all are on together ~8Kw max, relying on discrimination here)? Can 3 radial circuits, on 2.5 mm sq, be suppled via 32a MCB? In this case the remaining sockets in the utility room and garage would be left as part of the existing ring circuits.
Personally I do reckon it would be best to convert in to a new proper ring - just more effort on my part.
I've got over a week before I have to start crawling around roofspace and doing this work, and I reckon it shouldn't take more than a day or two.
Thanks in advance for assistance.