I'm still working my way through the latest IEE regs (it's many years since I last had to do it) but I haven't yet seen anything about loading design. If the CU has a 100A isolator must I ensure that the sum of the MCB trip levels is less than 100A or can I use a statistical method (root of some of squares) to combine the max loads on the basis that they won't all be maximum at the same time? TIA



Dave


They can add up to more than 100A, and there's a formula. This is covered in the On-Site Guide, Appendix 1, Table 1B. Note the figures are a guideline only based on typical usage. If you have some situation where you know the figures are unsuitable, you must adjust for that situation.

Thanks Andy, I've borrowed the guide now and all makes sense - I'll read it over the weekend.

On a slightly different tack ... The new CU will be mounted on the house-side of a cavity wall, the other side is the garage. I propose to run the cables down the garage side of the wall and through the wall (in a piece of plastic pipe) straight into the back of the CU - 'any problems with this? I assume the tails and the load cables should be in separate "ducts"(?). I'm still not sure whether to run the tails to the gge CU in parallel with the house CU or to run them from a MCB in the house CU - any suggestions?

Dave

With due regard to cable grouping, ie don't squeeze 'em close together through that pipe leave plenty of space and don't bundle them up all neatly together. I'd probably keep the pairs for rings together but otherwsie distribute them through out the pipe.

Seems sensible.

What load is the garage CU likely to carry? Any big machine tools or heating? Just a light and a couple of 13A sockets for power hand tools I'd buy a bigger house CU and have it all in there. RCBO for the garage sockets or individual RCD sockets.

Dave brought next idea :

The word you are looking for is 'diversity'. Not all loads will be on at the same time, nor will all the loads be taking their maximum current.

The gge will have:

- a 3kW rotary 3-phase converter (probably needs a C or D rated 32A MCB for starting),

- a 2kW 3-phase inverter (16A MCB),

- a regular ring (32A RCD),

- a couple of non-RCD sockets (16A MCB)

- and lights (6A MCB). I'm keen to have the gge MCBs in the gge so I need a separate CU, I guess the load is sufficiently large that it's worth having the 2 CUs in parallel (?)

Dave

7kW or more, yes feed 'em in parallel with the henley blocks close to the meter.

Ahh - this is a "serious" garage installation, then ;-) Reasonable to reckon you could be pulling 7-8kW, being some 32A or more. For this amount of "juice" you want to think of the feed to the garage as a "submain": I'd want a 32A or 40A MCB in the CU, with the supply to the garage in an Appropriately Rated cable; design calculations might allow

6mmsq, depending on length and circumstances of run, but you want to keep voltage drop low on this submain and consider splashing out on 10mmsq. Depending on the physical run, it's just possible that PVC T&E would do (if the gge is attached to the house), but SWA is prolly more what you're looking at. The MCB in the main CU is only protecting the cable to the gge CU; from there, protection is provided for each individual circuit by the MCBs in each CU. You need to do the calcs on earth loop impedance quite carefully to size this cable, especially if you're going to use a Type C MCB in the main CU - since it takes longer to trip, the permissible cable run is lower (to make sure the earth loop impedance is low enough so it trips in sufficient time to protect the cable thermally and limit the voltage while an L-to-E fault persists). Basics of the calcs are well explained in the "standard" electrician's bibles; but this is territory beyond the Which? Guide To Electrics ;-)

HTH - Stefek

Thanks to all. I've had a slight rethink and will probably go for one CU in the garage (part of house) rather than 2 separate CUs. The only range I can find that will give me the mix I need (10 unprotected and 5 protected) is Proteus from CEF - any views on this range or suggestions for others?

Dave

If you're in the garage, you probably aren't short of room on the wall. In which case, you'll get most flexibility by using two CUs - say a

12way or 15way with 100A incomer switch for your 10 unprotected final circuits, and a 6way with an 80A RCD incomer for the 5 circs you want on an RCD.

As they're close together, it's fine to run them "in parallel" by using a Henley Block (overgrown junction box) to take the meter tails in and feed out tails to both CUs; you only need the "submain" thing with its own short-circuit and overcurrent protection if the second CU is "some distance" from the main incoming supply fuse, where "some distance" is a quite short piece of string, around 3m as a typical guideline - actual limits depend both on Real Engineering Calculations about how long it'll take the fuse to blow, how high a current will flow until it does, and thus how hot the cable will get while the fuse is deciding to blow.

Not that the Proteus is a bad brand, or anything, just that you won't be tied to one particular make and have it filled up (or nearly so) right from the start.

Hope that's still helpful, rather than being a massive goalpost tour ending up where we first started!