The design of our new kitchen for our open-plan extension is slowly maturing and, having decided what induction hob and double built-under oven we want, I would be grateful for opinions on what power supply(/ies) to run to them. The specs are:

Hob: AEG IKB64401FB, Total Loading 7350W (/230V = 32A) Oven: AEG DUB331110M, Total Loading 5300W (/230V = 23A)

The route from the CU to the hob+oven is pretty straightforward: Up 1m inside an uninsulated stud wall, across 5m inside an uninsulated ceiling and down 1.5m behind uninsulated plasterboard.

Taking the IET OSG guidance on diversity for cooking appliances, the total supply requirements would be:

First 10A + 30% of remainder = 10 + ( ((32+23)-10) x 0.3) = 10 + 13.5 = 23.5A

If my understanding and calculations are correct a single 6mm2 going to a single 45A DP switch (a rare white one!):

formatting link
and dual appliance outlet plate:

formatting link
should suffice. The cable would be adequately protected by a 32A MCB.

However, for future proofing (and better/safer? operation) should I put two 6mm2 cables in instead, each with there own 32A MCB? Or perhaps a single 10mm2 with a 40A MCB? Running cable is easy at the moment as the ceiling is down and I have open access to the rear of the CU (which, whilst a bit tight for wiring, does have some spare ways).

Note that this open-plan extension is being done under building control and so, with the hob+oven being a new circuit and therefore notifiable, I plan to get an electrician in to do the work (and, more importantly, give me the necessary certificate for sign-off) however I wanted to give some thought myself to what we should do in advance of asking them, whoever that might be... @Adam: You're not travelling through North Wiltshire anytime soon are you? ;-)

Reply to
Mathew Newton
Loading thread data ...

I could be close in three weeks time. She will needs some convincing to go to Melksham and not Oswestry....

I suppose if Lilley's Cider shop at Frome is open she can be convinced.

How far from either are you?

Reply to
ARW

That seems unreasonable. In the winter, when starting for breakfast, I always put the hob to full power on four rings, to warm the kitchen. I think the cable rating, whatever the IET may say, should allow - at least - for any single large appliance, plus a family-size electric kettle, plus refrigeration, to be running at full power.

Reply to
Dr S Lartius

It does, but not for continuous use.

In this case you could not turn the hob on to warm the kitchen:-)

Reply to
ARW

At full load it might still take 15 minutes to flip the MCB?

Reply to
Fredxx

AEG IKB64401FB is an induction hob and will switch itself off almost immediately if no induction-compatible pans / load detected.

Ours is a slightly different model but limits maximum ("boost") power to

10 minutes.
Reply to
Reentrant

I'm in Malmesbury so around 30mins from Melksham and maybe nearly an hour from Frome so a bit of a trek?

Reply to
Mathew Newton

Only if you drive like a girl.

Reply to
ARW

She has just mentioned the caravan.

Reply to
ARW

:-)

All joking aside, if you don't mind a bit of a busman's holiday the job's yours.

You must hate it when customers say this, but I do think it's a straightforward one. As mentioned it's all in the same room with the CU and ceiling both readily accessible, and I just need to do the cutouts for the backboxes in the dot-and-dab wall (there's around 15-20mm free space for the cable run behind):

formatting link
I've already got some spare Wylex MCBs (32A and 40A), but no cable.

Reply to
Mathew Newton

My choice would be to over provide on the circuits.

The cost of the extra bits of cable etc. and labour now are minimal compared to the cost of doing it later should you need to for any reason.

Cheers

Dave R

Reply to
David

It sounds more fun than than spending my time with her in laws.

I would run two cables. I have plenty of 6mm T&E. Email me your details and we can have a proper chat. I was not intending to fetch power tools as we need the space in the car for the cider, her shoes, her spare shoes, her clothes and her spare clothes:-) Although it looks like you do not need them.