As fas as I can tell the fan oven is on its' own circuit.
>
> Been there from new, probably about 13 years.
> Not used as an oven usually (we have a combi) but weekly or more for the > grill.
>
> Cooking a chicken (to leave the combi microwave free) and at some point it
> tripped the breaker.
> Tried to reset the breaker and popped immediately.
> Turned the oven off and tried again, still popped the breaker.
> At that point I assume that only the control panel (with cooling fan)
> would be active.
Breaker = MCB, RCD or RCBO?
At the moment I am assuming that it is terminal, and probably not worth
> trying to repair a 13 year old oven.
> However I also assume that some testing is needed to confirm that it is > the oven.
The element is a wire in an earthed metal tube, filled with ceramic. Eventually the ceramic breaks down and you get a low resistance path to earth that trips the RCD/RCBO - maybe that only happens when things are hot, or when it's got damp through irregular use. It could be a neutral to earth fault that is still present when the oven is turned off.
Suggestions welcome.
Change the element. You may be able to let it cool, then turn on elements independently (grill / etc) and see if you can work out which one is tripping it. If any element is visibly drooping or out of shape, now is the time to change it.
Elements are a wear item and often readily available for not-very-much. I did my 25 year old oven recently - fitted a new fan motor too. New element was about £15, it was simple to do once I'd gained access to the back of the unit.
Theo