Yes, wire them all into the old cooker circuit. No problems at all > Don't
> use sockets/plugs, but FCUs. Ensure the correct fuses are used. Cooke > hoods
> and hobs are sufficiently fixed to not be run off a socket circuit > Indeed,
> I run many more appliances off dedicated radial circuits, includin > fridge
> freezer, washing machine, tumble dryer and dishwasher. In my case > however,
> I decided to run the cooker oven off the main ring, largely becaus > with all
> the other fixed appliances offloaded, there is loads of spare capacit > off
> it, and only the 2nd oven will be electric. Grill, main oven and ho > are > gas. >
> When installing, check the oven rating. It may need to be fused at a
> particular level (i.e. 13A, 16A or 20A). Ensure this is done, eithe > using
> an FCU (for 13A) or by dropping the MCB to that level. Some will be
> perfectly happy at 32A, but if it comes with a conventional plug, yo > MUST
> use a 13A FCU (unless instructions specifically allow 16A MCB instead > as
> would be the case in a European installation).
>
> However, even if the oven allows 32A, it is still safer to drop the MC > to
> the next value over the sum of the appliances you have installed. (i.e > 13A
> for the oven, 3A for the extractor, 0A for the gas hob means you coul > run
> off a 16A MCB, which is more likely to trip in a fault condition tha > an
> oversized 32A, oven if this would be technically allowed).
>
> Christian.
Thanks for the information. I think adding 2 FCUs (with labels an indicators) to the cooker circuit is the best way forward. The new ove is rated at 4.8kW, hob 100W and hood 260W so this is all well below th current (all-electric) cooker's rating.
Final questions - should the wiring for the FCUs be 4 sq mm or is 2. sufficient? And presumably the FCUs are connected before the cooke isolator, i.e. the isolator switches only the oven supply?
Cheers