I want to fit a socket on an exterior wall of my house for car vacuuming, etc. Leaving Part P aside, would it be ok to break into an existing ring, fit a fused spur and run a cable through the wall to the socket as a radial circuit? The socket of course would be IP66 with an integral RCD.
Yup - basically. You would ideally need a double pole isolation switch inside to allow it to be turned off, and also to electrically remove it from the system should it introduce a trip problem to the house in wet weather etc.
Note if the circuit you feed it from already has an RCD protecting it, you will derive no extra benefit from a second one (and they don't discriminate either - so if an event happens that cause a trip, any combination of one or both tripping could be the result)
I've got several PowerBreaker H92s for outside sockets, pond electrics, etc. [Mine are an earlier model, and look a bit different - but do the same job]
It's easy to switch them off, simply by pressing the Test button. AIUI, this then breaks both live and neutral.
Is that correct? I thought this was solved by having 'slow' and 'fast' trip RCDs so that the appropriate one blows first. Maybe that's only done to separate the 'whole house' RCD from the 'individual circuit' ones.
On Tuesday 12 February 2013 09:45 RobertL wrote in uk.d-i-y:
Yes - it's completely randome which one trips - probably both as they will have seen the current imbalance and started their trip sequence anyway.
The "fast trip" are 40mS (ie the "standard" RCD) and are the slowest permitted by the regs for the purposes of protecting someone who comes into contact with a live.
I am not aware of an RCD that can trip faster than 40mS.
The "slow type" you speak of are Type S Time delayed and are for use with TT (earth rod) installations and their purpose is protecting the cable against I2t (energy) overload in the event of a L-E fault. They do not offer suitable protection to people touching the live.
You can do this in some cases, but the "slow" RCD (aka Type S or time delayed) is not appropriate for protection against direct contact - so you could not use it to protect a socket circuit. So you are reduced to a normal speed 30mA trip RCD at the circuit origin, which leaves no scope to have a faster RCD downstream.
HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here.
All logos and trade names are the property of their respective owners.