Your proposed solution may be incorrect.
Regs limit the number of connections in a socket to 3 o 2 connections for the ring legs o 1 connection for 1 socket spur off the ring
You propose a choc-block to keep to 3 connection limit o The choc block would need to be 30/32A
---- two spurs to 2x 1G sockets can draw 2x 13A = 26A
---- two spurs to 2x 2G sockets can draw 4x 13A = 52A*
---- * obviously limited in the latter by 32A ring CPD o The cables feeding the choc block must be 30/32A
---- a spur to 2x 1G sockets is 26A or 1x FTE-2.5mm
---- a spur to 2x 2G sockets is 32A or 2x FTE-2.5mm
---- so link the choc-bloc by FTE-4mm or reroute legs o The choc block & cables take up a lot of space
---- I doubt it would fit even in a 47mm depth box
There are some alternatives.
- If you only require 13A in total from "two spurs".
a) If your existing socket is 1G (1-gang)... o Fit a Twin-1G metal backbox in place of the 1G socket
---- it is a single metal box with twin-1G fittings
---- separated by a metal plate which you push out o Fit a 1G Socket in the one side
---- into which your 2 ring legs connect o Fit a 1G Fused Outlet (FCU) into other side
---- run 3rd FTE-2.5mm to the socket next to it
---- run as many spurs as you want off this (13A fuse) o Maintains 3-wires into socket & good workmanship
b) If your existing socket is 2G (2-gang)... o Fit a 1G metal backbox next to the socket o Fit a 1G Fused Outlet (FCU) into it
---- run 3rd FTE-2.5mm to the socket next to it
---- run as many spurs as you want off this (13A fuse) o Maintains 3-wires into socket & good workmanship
- If you require 13A from each spur, 26A total.
o Fit a Twin 1G metal backbox in place of the 1G socket
---- it is a single metal box with twin-1G fittings
---- separated by a metal plate which you push out o Fit a 1G Socket in EACH side of the fitting o Ring leg #1 goes to LH socket, leg #2 to RH socket
---- this separates the original ring o Link the two sockets by FTE-2.5mm
---- this rejoins the ring o Spur #1 off LH socket, Spur #2 off RH socket o Maintains 3-wires into socket & good workmanship
However you may not have sufficient ring leg length.
It can be done similarly with surface mount boxes, but that may be problematic re ring cable length.
You CAN use a 30A junction box under floorboards: o The EXISTING socket become a spur o Your junction box then runs the 2 new spurs as a RING o You would need to link these 2 new spurs as a RING
The problem is accessibility: o Accessibility means an area never subject to furniture o Eg, a landing area, access via hole/floorboard
I would fit a twin-1G box in place of a 1G/2G socket, fit FCU in one side & 1G skt in other. Then run as many spurs as you like off the FCU subject to 13A load limit.
Alternatively extend the ring properly - as a ring.
I think I read your question correctly.