Can anyone help with the wiring instructions for a 3 port Diverter Valve ? The valve (not a mid-position) was supplied from a Italian company and the intructions do not match the wire colours.
There are 5 wires.
Yellow/Green Blue Red Grey White
I assume that some of the wires become live when the valve is in different positions.
Thanks
Richard
Didn't find your answer? Ask the community — no account required.
R
Ron Lowe
If the wire colours don't match the documentation, then you need to figure it out from first principles.
Can you open the lid of the motor assembly, and just look at what they connect to?
If not, then you will need an ohm-meter.
Check yellow / green 0-Ohm to the body. This will be the earth. Equivilant to Yellow / Green on a standard honeywell valve
Then look for a couple of K ohms between 2 wires. ( perhaps the Blue and Red ). That will be the motor. Equivilant to Blue / Brown on a honeywell.
The remaining pair will be the microswitch. They should be open-circuit to all the other wires.
They should be open-circuit to each other with the valve de-energised. To fully test the microswitch, you'd then need to apply 240 to the motor, and observe the microswitch pair on the ohm-meter. They will go short ( 0-Ohm ) when the valve is fully opened. Equivilant to Orange / Grey on a honeywell.
E
Ed Sirett
This is a _three_ port valve. It's close to the colours use by Honeywell if red were orange. The OP should read the main FAQ and see if the unit looks like it is wired up Honeywell style with red for orange.
Join the Discussion
Have something to add? Share your thoughts — no account required.
Didn't find your answer?
Ask the community — no account required
Report Content
You are reporting this content to the moderators. They will look at it
ASAP.