Advice re Electric shower please

Apr 04, 2004 3 Replies

I realise that this is UK diy, but please bear with me



I need to know how to work out whether the following is viable or not.



My supply in Spain is 15A/3.5KW which can be updraded to 25A/5.7KW.



Do you think it is possible and safe to run an electric shower of around 6KW. If not what size shower could I run and also can you tell me how the figures are found



Many thanks


The figures for the protection are ( fuse or mcb ) are found by dividing the voltage by the power to give a figure in amps.For your 6KW shower a current of

25Amps would flow based on a 240 Volt supply. You would need a larger mcb than 25Amps in the UK showers are generally protected by a 40A mcb.You also need to consider the size of the cable and the length of the cable run.

Is it possible that this is the rating of her main fuse / branch circuit?

If this is the case then a very simple answer is available:

You can't run a 6kW shower on a 5.7kW supply nor, obviously, a 3.5kW supply.

I'd also suspect that even in Spain, 6kW isn't going to make a particularly hot / fast shower.

Hwyl!

M.

On Thu, 08 Apr 2004 23:23:37 +0100, in uk.d-i-y Martin Angove strung together this:

I was thinking along these lines but I lost the thread! Now it's back I'll comment on it, ISTR someone else on here mentioning the Spanish electrics only having a 20A supply to the property. I think *any* electric heating is going to be a no-no.