light won't light

Dec 20, 2019 20 Replies
Saved reading
Jump to replies (20)

The light in the laundry room stops working after worker had worked on the ceiling in the next room.



There are two wires coming in to the light (or one in one out). Before I flip the switch, both wires are not charged as tested by a tester. After flipping the switch, both are charged. Yet, the light just won't light.



I removed the light and plug it in to a socket, it works.



Question:


1) did the test (both wires not charged and then charged after flipping the switch) I do make sense?


2) how could the work in the other room affect the light next room? I do see that there are three wires in the switch box, none of them neutral or ground. They are all live wires. Two on one side of the switch, one on the other side. The two are charged, the other is only charged after the switch is flipped.


This test is with the light removed? You have one cable, with two conductors plus a ground wire? By charged, do you mean that you have 120V on both, or some other, lower voltage? What are you connecting the other side of the meter to? Ground?

I put a dimmer on the dining room light, got interrrupted in the middle for a long time, then didn't know why the range hood didn't work. The wire for the range hood came out of the box with the dining room light switch. Of course the wall was right between the rooms.

You're using a real volt meter, not a neon light or something? The lightbulb is not in the socket when you are testing the voltage to it?

This is the switch for the light that does not work?

The "two are charged" when the switch is not flipped, but are both charged when the switch is flipped?

Is there more than one switch controlling the light in hte laundry room? Not very common but would account for there being 3 wires to the switch.

Alternate question, are the two that are charged directly conneded outside the switch, by a continuous piece of copper, or are they connected inside the switch. (I'm assuming one is connected to the other and the second one is hot only because it's connected. That's probably true.)

The worker damaged the neutral connection somewhere. The "juice" is getting in, but is not getting out.

I would agree, IF he's did his testing with the light in the circuit. But if not, the above does not explain how he says he has TWO wires that are energized.

I used a neon light tester. The light bulb was in the fixture. The light worked when both the fixture and the light bulb were removed and connected to another circuit.

Yes and yes.

No.

They are connected directly to the switch, two wires going into one side of the switch and being tightened by a switch screw, the other going to the other side of the switch.

No. Tested when the light tube was in the fixture. There is no ground wire, no neutral inside the switch box. I used a neon tester.

Somethin's not right. There should NOT be 2 wires under one screw. What wires are in the box with the switch - and what colours are on each screw of the switch? If there is power on one black wire at the switch, and no power on either wire at the socket with the bulb removed and the switch off you should have 1 black wire on each switch screw and 2 white wires wire-nutted in the switch box. If you have power on one black wire at the socket with the switch off and the bulb removed there will be 2 wires (1 black and one white) at the switch and 4 wires in the box at the light. The blach live wire will be connected to the white of the other pair. The white of the "feed" pair will be connected to the silver screw of the socket or the white wire of the fixture. The black wire of the "dead" or switch pair connects to the dark screw or the black wire of the fixture. The white leads to the "shell" of the socket, the black to the center "pin" or "spring". The two wires at the switch connect to the switch, with the white wire marked with a black tape, marker, or shrink-tube to identify it as "HOT". Bare wires are connected to the box at both locations, and to the freen wire if it exists on the lamp fixture.

Is this a flourescent lamp? If so you MUST disconnect the black wire from the fixture before testing - removing the tube does not accomplish anything short of insuring it won't light. The "ballast" has to be taken out of the circuit.

Perhaps you should have a qualified electrician working on it - but if you follow my instructions you WILL get the problem solved and it WILL be safe and it WILL be "legal". Where I said "bare wire in my last post it could also be "green"

That's NO GOOD. It can show something as hot that isn't, just because something nearby is hot. Once you have one mistake in your perception of things, you'll never figure out the truth.

So there's nothing wrong with the lightbulb but using neon, you haven't learned a thing about the socket wires.

You need a VOM, a volt-ohmmeter. HarborFreight has them for 4 or 5 dollars. If that isn't handy, Home Depot has them for 10 or 20.

You're going to have to get a real meter, do all the same measurements, and if necessary, come back here with useful results.

$10 is a small investment for something this important, considering what electricians charge, and that a meter can last you 60 or 100 years.

Try to get a package of jumper wires too, with alligator clips on each end, so that you can connect the black wire from the meter to another location, such as a ground, and only have to pay attention to the red proble.

!!! While analog meters, with a moving needle, have an advantage in a few situations, if you're only going to have one meter, I think digital is much better and much more useful.

Don't get a battery tester, don't get non-contact.

This, or something that looks like this, only $10:

formatting link
Note that there is one set of settings for AC and one for DC. Try to set things right before touching the leads to the wires. Most meters have over-voltage protection now but it's good practice, and some day you may be using a meter without that.

formatting link
The more expensive ones have options you'll probably never use.

Jumper wires, 1000 uses:

formatting link

Clare is probably right. One of the two wires to the lightbulb is a neutral, but if it is cut somewhere, the voltage comes in through the hot, goes through the lightbulb and makes the part of the neutral wire conneecte to the lightbulb hot also.

If you take out the light bulb and especially if you use a real meter, not a practically worthless neon tester, you'll see that one side of hte light fixture is dead. Since it is dead**, you can use the ohmmeter part of the vom to check the resistance between the dead wire and some other ground. If the neutral wire is cut, the resistance will be infiniite.

**If you try to measure the resistance between a hot wire and ground, you may burn out your meter, or even melt parts. But if you do this often, some day you will mess up. Try not to be standing on a ladder when you do this.

This is the laundry room. Is it finished, a ceiling?

Did the light used to work? Any work done in the laundry room or nearby lately? Like drilling, cutting, or sawing?

That's why both wires tested hot. Looks like the neutral is disconnected. With the neutral disconnected, no current flows and both sides of the load will be at the same potential. Since you say just two wires enter the light, the only way I can see that explains all that you reported is this. Power comes to fixture A in the other room that was worked on. From there, a cable goes to the switch that works fixture B, the one that doesn't work now. One wire of that cable is connected to incoming power hot at fixture A location. That wire is connected to one side of the switch, the other wire connects to the other side of the switch. Back a fixture A, another cable runs over to fixture B, the one that won't light now. One wire of that cable connects to the above wire coming from the switch, the other to the neutral. If that neutral connection was undone at the fixture A location, it would explain what you are seeing.

The light

Where do the two wires go? If what I say above is right, one wire from the side with two wires and the wire from the other side of the switchf should be in one cable. The other wire? Is there another switch in that box that it goes too, for example, to power it?

IDK what kind of switch that is, but if it's a simple screw that two wires are under, that's not allowed. If it's a back stab it can have two wires, but those really suck and I would not use. If it's the kind that wires can enter from the back and go under a plate with a screw, then I think two wires are allowed.

I would investigate the other location where work was just done and look for a cable that heads over towards the non-working fixture. Look for a neutral that's not connected. Even if it looks connected, eg has a wire nut, take it off, make sure they really are twisted together, etc.

Actually that problem typically occurs with a VOM with a high impedance. You could use a $150 Fluke which is a very real meter and see spurious voltage. You won't see it with an old meter with a needle movement, because it's not high impedance. I've never seen it with a cheap neon tester either, they take substantial voltage to light, eg 90V, and do pass some amount of current, so I think it's unlikely you could get it to light from spurious voltage due to a nearby cable. The non-contact type testers could light.

The most likely is that which Clare noted before; the neutral in the worked-on box wasn't reconnected.

If you can see the obvious issue there as he suggests, then you're good to go. If not, since the issue appears to have been caused by the work; I'd suggest get them back to fix the problem they created.

What was the purpose of their work just out of curiosity (altho that might have some bearing that might make understanding what happened simpler from afar).

I have seen the neon testers light up with no real current on the wires.

Where I worked many wires were in conduit and you could disconnect each end and the neon tester would light from one wire to the ground (conduit). A Fluke meter would show about 115 volts. My 'trusty' Simpson 260 analog would show about 75 volts on the 250 volt scale. One way I found to tell if the voltage was 'induced' was to start off on the highest scale of the Simpson, then switch to the lower ranges. If induced, the meter would stay about the same physical place on the scale. If 'real' it would show the same actual voltage. Some of the wires had enough current on them they would give you a very bad shock.

Some switches and relay contacts had capacitors and resistors across them to supress arking. The neon testes could be fooled by those.

Like I have said in a few other posts, I can not spell any better than the people in England. :-)

My computer spell checker is not much better.

[snip]

The disconnected neutral acts as an antenna and picks up the voltage of the nearby energized wire.

Actually he CAN do the whole test with nothing but a proper "neon tester" desighned for the job

No - a proper neon tester was actually the troubleshooting tool of choice for many professionalelectricians for decades. BUT - you have to understand it and how to use it.

That's right. Neutral was disconnected somewhere after the light. It's been fixed and is now working. Thanks to everyone who helped me.

Yes. Neutral needed to be reconnected.

Replacing kitchen ceiling was the work.

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required