Vaillant eco Tec plus

Sep 09, 2025 Last reply: 10 months ago 6 Replies

I had a Vaillant eco Tec plus 4/8 fitted in Spring this year before the £250 penalty was imposed.



Since the heating has been off and it has been used for Hot Water only it has stopped working a couple of time with a flow/return sensor fault. Re-setting it sorted it out both times.



The plumber said it is because it only has a light load when heating water only and the low flow/return temperature difference causes problems.



Does this make sense or should I be asking for further investigations to be carried out?


I would think that heating water is the heavier load, 24 or 28 kW rather than the five to one kilowatts when heating say in Spring of Fall...

Thomas Prufer

Return sensor on the hot water ?

a partially blocked or scaled up DHW heat exchanger can cause this issue

Did the boiler engineer fit a limebeater to the cold water supply to said boiler?

S.

P.S did the boiler engineer powerflush the rads and fit a Magnaclean before commissioning the boiler?

very important to prevent the iron oxide (magnetite) from finding its way from the radiators to the DHW heat exchanger and blocking it.

PLus you need corrosion inhibitor installed at each annual service.

Only if you have a hot water tank, not on a combi boiler supplying hot water.

It's recommended that a power flush is performed before a new boiler is installed. If it running a hot water cylinder a magnetic filter should have also been fitted to meet the Vaillant 10 year guarantee conditions.

The 4/8 being a high power output system boiler?

Nope very little! (at least assuming those are the exact phrases used)

DHW recovery is usually a fairly high load for a shortish period of time. Compared with CH in the warmer months, which is more of a gentle trickle of heat for a long period.

Also flow/return temperatures have nothing to do with flow / return sensors - which detect flow not temperature.

Do you have the fault codes that were displayed?

Possibly... :-)

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required