TT earth rod indoors?

Jan 18, 2022 Last reply: 4 years ago 3 Replies
Saved reading

First reply

ARW

I cannot see any reason why you cannot leave them where they are. But they will need to be in an inspection pit not under concrete.

Read the full reply

I'm starting a kitchen extension which will include where the earth rods are hammered into the mud.



Will I have to move them outdoors?



Or can I concrete them in where they are?



formatting link


I cannot see any reason why you cannot leave them where they are.

But they will need to be in an inspection pit not under concrete.

You would need to consider local soil conditions to asses the impact of that. The rod impedance will tend to rise in dry conditions, so you need to be confident that the tip of the rod is going to stay in adequate contact with damp enough soil, even if the whole thing is permanently sheltered from the rain.

So round here for example (heavy clay) once you are more than 3' down the moisture content is fairly constant year round. In a better draining soil that might not be the case.

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?