My garage is en block with others, across the road from the house. It is fed with SWA cable running from a junction box at the front of the house, and under the pavement, road, and garage hardstanding to a CU in the garage. There is no separate earth at the garage end. The house supply is TN-C-S.
This radial is fed from the house CU, on a bank of circuit-breakers (labelled Garage, Sockets, Sockets Down, Sockets Down) protected by an 80A RCD. The Garage breaker is labelled Legrand B16.
The total run is about 17 to 18m, and the cable outer diameter is a little over 12mm, and is presumably 3-core.
My question is, given the underground run of the SWA, how much current could I draw for long periods, say 12 to 15 hours, without risk of the cable deteriorating over time?
A secondary question would be, what is the maximum current capacity of the cable in these circumstances?
TIA
Didn't find your answer? Ask the community — no account required.
D
David
A 1.5mm2 3 core SWA cable is typically about 12mm dia and will have a maximum current carrying capacity of about 15A, but I wouldn't normally want to exceed 10A max.
A
Andy Burns
Or could be 2.5mm^2 two core if the armour.
Higher if XLPE ... depending on installation method.
C
charles
I read it as 18A from the tables. But, with a 10A load, you'll be dropping
5v on that run. What are you planning to do?
J
John Rumm
12mm is probably 1.5mm^2 - see the table here:
formatting link
It might be two core - normally one would export the earth on the armour wires. However if you export a TN-C-S earth, one should also export the equipotential zone as well - and that would require something with enough CSA to function as a main bonding conductor as well.
(you could of course insulate the earth at the destination and add a RCD there, with a local earth spike making it a TT install)
The long term current limit is set by the insulation temperature.
There are two common types of SWA - PVC insulated (so called "thermoplastic insulation"), and XLPE ("thermosetting insulation").
The former has a maximum conductor temperature of 70 deg C, the latter
90 deg C.
So XLPE can carry a higher current - but only in cases where the termination equipment is also capable of operating with 90 deg conductor temps.
The "buried in ground" (directly, on in conduit) is a reference method D install. For a PVC SWA that actually *increases* the current carrying capacity a little bit, and for XLPE it reduces it a bit.
So from table 4D4A - 70 deg C multicore armoured cables A reference method C install would allow 21A, and a reference method D would allow 22A
For the XLPE cable, that would be (from table 4E3B) reference method C:
27A, and method D: 25A
So with PVC cable and a 20A MCB, you could run at the full 20A, and with XLPE you could use a 25A MCB if you can find one.
However the voltage drop might be borderline, since when operating at max temp the voltage drop per meter per amp is 29mV at 70, or 31mV at
That would translate to 10.4V or 11.2V assuming 18m of cable. (you can have 11.5V for normal circuits, but only 6.9V for lighting circuits)
So either is fine for "normal" use. For charging an EV, then a "granny" charger is ok, you might also be able to go for 5+ kW charger, but not the full 7.3kW of a 32A circuit.
S
Spike
Many thanks for the full and interesting reply, and thanks too to all those that responded.
I would have answered your post sooner, but was waiting for the afternoon shade to come round so I could take the cover off the wall-mounted junction box after isolating the circuit.
The diameter of the SWA is 16.8mm and not as previously stated. It contains three cores of red, blue, and yellow. These individual cores are very close to 4mm diameter. Red is connected to house red, blue to house blue, and yellow is connected to both the house green/yellow and the tab of a washer that holds the fixing gland in place. All of these conductors look to be the same diameter.
From the link you gave, this would strongly indicate conductors of 6mm^2 with a cable current rating of 42A (PVC) or 53A (XPLE) presumably in free air.
This is far more current than might be required, and presumably this cable could be run at 10 to 16A continuously (although the latter isn’t a likely modus), the circuit breaker being rated at 16A.
J
John Rumm
Yup, today was not a good one to be sat in the sun! It was 29 for a bit here.
Yup SWA cores are normally all the same diameter (and three core would typically carry three phase, so they would need to be!)
Yup 6mm^2 gives far more options. Also by combining the armour with a core, that also gives you enough area of CPC to function as a main bonding conductor as well since you have 6mm^2 of core and 23mm^2 [1] of armour, which you can divide by 2.255 to get the "copper equivalent" size of 10.2mm^2, or over 20mm^2 in total for your CPC. Which is plenty for a main bond [2] to pass the adiabatic heating under fault conditions check [3]
[1]
formatting link
[2]
formatting link
[3]
formatting link
In reality you could pull a bit more than 16A without tripping the breaker, or could change it for a larger one with no worries.
S
Spike
Many thanks once again for a full and interesting reply. It would seem that this cable has been well spec’d and installed. With the right breakers in the house and garage CUs, it could carry 7kW if necessary.
One slight fly in the ointment is that the thin steel nut that holds the gland to the house box on the outside wall appears to have corroded and delaminated, although the brass earthing washer underneath it and everything else there seems fine. I can see no evidence of water ingress.
Replacing this with a proper earthing nut seems to be a straightforward exercise, so I’ll get one ordered toot sweet.
Thanks for the links, they made interesting reading!
J
John Rumm
Indeed... it makes sense when installing feeds to outbuildings to overspec the cable since it is a one off cost, and often small compared to the cost of the whole job.
Yup those skinny nuts are a bit crap really. Hence the number of after market nuts that do a better job and make it easer to terminate the earth connection without needing to rely on the "banjo" tag. Some examples here:
formatting link
Only thing is you can't do it without disconnecting all the wires :-)