New radiator valves

Oct 23, 2025 Last reply: 8 months ago 6 Replies

Fitting new rad valves, and there are two options.


  1. Use an olive splitter, and fit a new olive.


  1. Use the 'nut' part of the old valve. This way the olive doesn't need to be removed.



Which is likely to cause the fewest problems?



It depends whether the stub of pipe is short enough to allow the olive to "seat" - if it does (and cosmetics are not relevant) I would choose option 2 (with a smear of boss white, of course). Option 1 has the risk of nicking the pipe, or the pipe having been slightly compressed.

You can also get olive pullers that may do less damage to the pipe.

formatting link
Random Ebay example
formatting link
I would replace the olive and use the nut with the new valve.

You may find that your new valve is a different size to the existing valve, especially if it is very old. You may have to lengthening the existing connecting pipe. I had to do this on my 20 year old system.

That's interesting, but I think this is better:

formatting link

Depends on the circumstances.

If:

a) The new valve has the same size backnut and pipe fitting as the old, and

b) If the new valves pipe recess is deep enough that the old olive makes good contact with the sealing face, and

c) the result is cosmetically acceptable

Then go with option 2.

Otherwise you might need option 1, or the even more involved option of changing the valve stub in the rad itself.

Older valves used 3/4" BSP nuts, and newer ones tend to use 1/2". Also older stubs often had machines ends designed to mate with a cone fitting on the valve body. New ones are often designed as plain pipe ends, and the valve has compression fittings on the pipe inlet, and the outlet to the rad. The newer style gives a bit more flexibility in valve spacing from the rad.

I should have said that we're also changing all the radiators, too.

Consider increasing the size of the radiators which may/will increase the efficiency of your boiler/system by allowing you to decrease the flow temperature. This assumes a modern condensing boiler or heat pump.

You may find that increasing a type 11 with a type 21 or type 22, or a

22 with 33 etc. results in minimal adjustment to the tails.