Why do "builders" seem to think they are technically competent to design and install services? I've lost count of the number of defects I've encountered with gas, electrics, water etc. Enquiring of the householder often elicits the reponse "oh the builder installed it that way as he couldn't get a sparky/plumber/gas installer etc when he was doing the extension etc.
The up-to-date rating for 'clipped direct' conditions T&E is 20A, not
19.5, see Table 4D5A. The up-rating took place in Amendment no. 1 to BS
7671:2001, released in 2002, see
formatting link
there is no derating for "chased in wall" unless any special thermally insulating plasters are used.
From the aforementioned Amendment:
"433-02-04 For a ring final circuit protected by a 30 A or 32 A protective device complying with BS 88, BS 1361, BS 3036, BS EN 60898, BS EN 60947-2 or BS EN 61009-1 (RCBO) and supplying accessories to BS 1363 and wired with copper conductors, the minimum cross-sectional area of both phase and neutral conductors is 2.5 mm2 except for two-core mineral insulated cables to BS 6207 for which the minimum is 1.5 mm2. Such ring final circuits are deemed to meet the requirements of Regulation 433-02-01 if the current-carrying capacity (Iz) of the cable is not less than 20 A, and if, under the intended conditions of use, the load current in any part of the ring is unlikely to exceed for long periods the current-carrying capacity (Iz) of the cable."
This clearly makes it impossible to design a compliant ring in 1.5mm^2 PVC T&E cable.
The condition causing greatest fire risk is if the cable CPC (earth) is not adequately protected in the event of an earth fault. The combination of a 30A rewireable fuse as the protective device and the old 2.5 T&E, which only had a 1mm^2 CPC, can cause this situation to arise for rings over a certain length if the supply Ze is toward the upper limit. An earth fault occurs, there's not enough current flowing to blow the fuse quickly, the cable CPC overheats and possibly catches fire as it protects the fuse.
Thus it was realised sometime around the late 70s that lots of inadequately protected rings had been installed. BS 6004 was amended to require a 1.5mm^2 CPC.
Moral - never re-use old 2.5 T&E cable, at least not without checking the CPC size.
Thinking about it you're right I have got it wrong, 10mm indeed (!), probably more like 30mm....
IMM, it's you who plainly don't know what a RING MAIN is and how different it is to a RING CIRCUIT (or ring final circuit) - for one, a 'main' is normally out in the road and a 'circuit' is in a building !
Wire size determines temp rise, and permissible temp rise depends on insulation material, as well as what safety margins are applied. So in the days of rubber wiring, wires were thinner, and often got warm.
Go back further, and some wires ran positively hot, and it was considered normal. In the 50s hot wiring on a then old installation was just accepted many a time.
It can safely carry 10 amps on its own. Unfortunately cables nowadays seem to be grouped together in bunches, stuffed along RSJs and tacked in a myriad of other unsafe places. I know this because I've just ripped out the wiring from a house that was completely rewired in the 80s and the number of burnt bits of insulation was eye-opening. How the place hadn't burnt to the ground I don't know. Using 1.5mm allows more underrating and is safer for little extra cost.
A few more people not cutting corners in the past and we wouldn't have been lumbered with Part P.