Why do "builders" seem to think they are technically competent to design and install services? I've lost count of the number of defects I've encountered with gas, electrics, water etc. Enquiring of the householder often elicits the reponse "oh the builder installed it that way as he couldn't get a sparky/plumber/gas installer etc when he was doing the extension etc.

Reply to
John
Loading thread data ...

circuit

Definitely, I'm not saying they should either, hence my last point.

Reply to
StealthUK

The up-to-date rating for 'clipped direct' conditions T&E is 20A, not

19.5, see Table 4D5A. The up-rating took place in Amendment no. 1 to BS 7671:2001, released in 2002, see
formatting link
there is no derating for "chased in wall" unless any special thermally insulating plasters are used.

From the aforementioned Amendment:

"433-02-04 For a ring final circuit protected by a 30 A or 32 A protective device complying with BS 88, BS 1361, BS 3036, BS EN 60898, BS EN 60947-2 or BS EN 61009-1 (RCBO) and supplying accessories to BS 1363 and wired with copper conductors, the minimum cross-sectional area of both phase and neutral conductors is 2.5 mm2 except for two-core mineral insulated cables to BS 6207 for which the minimum is 1.5 mm2. Such ring final circuits are deemed to meet the requirements of Regulation 433-02-01 if the current-carrying capacity (Iz) of the cable is not less than 20 A, and if, under the intended conditions of use, the load current in any part of the ring is unlikely to exceed for long periods the current-carrying capacity (Iz) of the cable."

This clearly makes it impossible to design a compliant ring in 1.5mm^2 PVC T&E cable.

The condition causing greatest fire risk is if the cable CPC (earth) is not adequately protected in the event of an earth fault. The combination of a 30A rewireable fuse as the protective device and the old 2.5 T&E, which only had a 1mm^2 CPC, can cause this situation to arise for rings over a certain length if the supply Ze is toward the upper limit. An earth fault occurs, there's not enough current flowing to blow the fuse quickly, the cable CPC overheats and possibly catches fire as it protects the fuse.

Thus it was realised sometime around the late 70s that lots of inadequately protected rings had been installed. BS 6004 was amended to require a 1.5mm^2 CPC.

Moral - never re-use old 2.5 T&E cable, at least not without checking the CPC size.

Reply to
Andy Wade

Mr Cranium rambling again.

_________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download

formatting link
to open account

Reply to
Doctor Evil

He never denied it when confronted.

_________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download

formatting link
to open account

Reply to
Doctor Evil

Obvious, that is why 2.5 is standard. Some turkey named Jerry says it has to be 10mm. Yes, 10mm cable in a ring main.

Only on the Internet you get this.

_________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download

formatting link
to open account

Reply to
Doctor Evil

I hope not. Modern lighting uses a lot more power than in the old days and

1.5mm isn't that much more expensive.

IMHO 1mm stuff is only suitable for fire alarms and so on.

Reply to
Mike

A 3kw kettle will work fine off of 1.5mm cable, it's capable of handling

3.6kw.
Reply to
Kaiser

Thinking about it you're right I have got it wrong, 10mm indeed (!), probably more like 30mm....

IMM, it's you who plainly don't know what a RING MAIN is and how different it is to a RING CIRCUIT (or ring final circuit) - for one, a 'main' is normally out in the road and a 'circuit' is in a building !

Reply to
:::Jerry::::

He didn't need to denied it, the point that you removed the qualifying statement and in so doing you were able to twist what he said.

Reply to
:::Jerry::::

1mm can safely carry 10 Amps, and as most lighting circuits are protected by a 6 amp fuse/mcb, 1mm is quite safe to use.
Reply to
Dave Jones

Will it handle the 3kW electric fire as well, and TV?

_________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download

formatting link
to open account

Reply to
Doctor Evil

Let see, 3kw fire + 3kw kettle + 1000w TV = 7kw.

So a 1.5mm ring would be capable of handling 7.2kw.

Yes.

Reply to
Kaiser

device

1.5mm^2

Right, though they can be made perfectly safe by fitting a 20A mcb.

NT

Reply to
bigcat

On Thu, 3 Feb 2005 19:24:29 -0000, "Doctor Evil" strung together this:

We're not on the internet, which you probably already knew as you allegedly invented TCP\IP and everything thereafter.

Reply to
Lurch

Rated to that, its capable of a lot more.

And I've never seen a 1kW tv before! Even all valve colour dropper resistor sets came nowhere near that.

NT

Reply to
bigcat

-- snip drivel

Reply to
snip drivel

Wire size determines temp rise, and permissible temp rise depends on insulation material, as well as what safety margins are applied. So in the days of rubber wiring, wires were thinner, and often got warm.

Go back further, and some wires ran positively hot, and it was considered normal. In the 50s hot wiring on a then old installation was just accepted many a time.

I wonder what size Edwardian steel wiring was?

Snowdrops can be deluged by rainfall.

NT

Reply to
bigcat

I was just using 1kw as an extreme example, As not sure what every TV's requires.

Reply to
Kaiser

It can safely carry 10 amps on its own. Unfortunately cables nowadays seem to be grouped together in bunches, stuffed along RSJs and tacked in a myriad of other unsafe places. I know this because I've just ripped out the wiring from a house that was completely rewired in the 80s and the number of burnt bits of insulation was eye-opening. How the place hadn't burnt to the ground I don't know. Using 1.5mm allows more underrating and is safer for little extra cost.