Hot Tub Supply

Do I need a 20amp fused spur supply for a Hot Tub installation ?

Reply to
Ray
Loading thread data ...

Whats the rating plate on the hot tub heater say? I suspect the answer will be no though, as a 20A load on a spur on a ring isnt really a good idea..

NT

Reply to
meow2222

Have not bought the hot tub yet just getting the electrics sorted.

Supply is coming direct from the CU, it is 4mm armoured cable going to an outside log cabin.

Reply to
Ray

So, do you think we're all clairvoyants? Why not ask the hot tub supplier what kind of supply it needs?

I can see from my crystal ball that you'll probably top post again.

MBQ

Reply to
manatbandq

Might be limited on Voltage drop. Max length is 4% of 230V = 9.2V

4mm² is 11mV/A/m which makes 9.2V/0.22V = 41m. So probably OK.
Reply to
Ed Sirett

Distance from CU is 20 metres.

Reply to
Ray

What earthing system are you using for that Log Cabin?

Reply to
zikkimalambo

Have you thought to ask the supplier/manufacturer?

Reply to
The Wanderer

How do you know that 4mm armoured will be adequate?

Owain

Reply to
Owain

My crystal ball was correct.

MBQ

Reply to
manatbandq