Electrical installation in a cloakroom

I just want to check on whether there are any specific requirements for the electrical installation in a cloakroom.

This has a WC and handbasin only, no shower etc.

As I read it in Section 601 of BS7671, the room would not count as a bathroom for that reason.

This would appear to make the rules the same as for any other, but I may have missed something somewhere else.

However, is there a requirement to bond the radiator?

Are there any requirements for the light switch? The present one is a pull cord, and I could not find a reason that it needs to be, other than perhaps the original electrician was lazy. Perhaps there was an earlier regulation that applied in the 80s?

Given the above, I would also assume no specific luminaire IP requirements?

Reply to
Andy Hall
Loading thread data ...

I agree

I don't think so.

Don't think so.

None specific, but "suitable for the location" (how bad is your aim :-))

Owain

Reply to
Owain

Correct.

Not unless Reg. 413-02-04 (i) requires it, which is most unlikely if you have modern MCB/RCD protection.

Main boding would of course apply to any metal services rising in this room, but you haven't mentioned that, so I doubt it applies.

No, and not that I'm aware of.

No, other than general suitability of all equipment for its environment.

Reply to
Andy Wade

Yes it is and supply in TN-C-S.

No they aren't in there.

Good. I couldn't think of a reason.

Sure. many thanks

Reply to
Andy Hall

Good. thanks

Well I wasn't thinking of a pencil beam to illuminate it. Actually a wide angle spotlight would be needed of course.....