bathroom lighting electrics question

About to install a "mirror light" over the washbasin in the bathroom. It is a mirror with a metal box on the back containing 2 compact fluorescent G23 lights that shine through un-mirrored areas of the mirror glass. It is rated IP44. There is an earth connection within the box. The light is switched by a short pull cord.

The instructions that come with the light say "This mirror should be fitted to a lighting supply protected by a 5 amp fuse or equivalent circuit breaker. If fitting in a bathroom the mirror should be connected to a supply protected by a 30mA RCD. "

The instructions also contain a diagram showing the bathroom zones, with a Zone 2 being defined for the area within a 60cm radius of the basin tap. Zone 1 is defined as requiring IP45 or better - with mains voltage fittings requiring a separate circuit and a 30Ma RCD, with Zone 2 requiring IP44 or better.

The instructions however make no mention of supplementary bonding... ..................

The elctrical installation has PME earthing. There a a "split" Consumer Unit, with only power sockets that serve the outside of the house protected.

All pipework in the bathroom is plastic. The IP44 ceiling light in the bathroom is in Zone3 (2.7 meter ceiling) as is the bathroom extractor fan. These are both on the same curcuit, with a MK 3 pole lockable isolator sitting between them. The light switch and the isolator are outside the room. The fan is about to bemade separately switchable via a pull-cord.

My question is: Is protecting the "mirror light" with a RCD a 'sensible' thing to do in my situation?

I don't really want to have the ceiling light protected, so it would mean either a separate curcuit from the protected side of the CU (if that is allowed) for the "mirror light" - along with supplementary bonding to the ceiling light, or putting in some form of RCD spur (TLC's Order Codes CM 4904 / BR H92 ) ...and finding somewhere to put it and regularly test it !) specifically for the mirror light.

Ray

Reply to
Ray Holden
Loading thread data ...

It will need supplementary bonding as it has an earth terminal. However, with plastic pipework, there might not be another fitting in the room that requires it. You shouldn't supplementary bond metal baths or radiators fed by plastic pipe.

That sounds all wrong. Zoning is in relation to the shower tray or bath tub.

This is what you should do. The manufacturer's instructions say it should have an RCD to be suitable for bathroom use, so this overrides any general requirement in the regulations.

Whilst you are there, you may wish to rejig your consumer unit so that all socket circuits (except the fridge/freezer) are RCD protected. This greatly improves the safety of the installation.

Christian.

Reply to
Christian McArdle

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.