Is a ground wire screwed into a wood stud actually doing anything?

Oct 11, 2026 Last reply: 9 hours ago 5 Replies
Saved reading

First reply

PrairieNic89

Wood doesn't conduct, so you're right that the connection is doing nothing. A ground wire's whole job is to provide a low-resistance path back to the panel so that if a hot wire touches metal somewhere, the fault current has somewhere to go and the breaker trips fast instead of…

Read the full reply

So I was poking around behind my workshop wall trying to figure out why my GFCI kept tripping, and I found the ground wire from the circuit just terminated on a ring lug and screwed straight into the stud with a wood screw. Like, directly into bare pine. Nothing else, no strap, no box, just the screw biting into wood.



I always thought ground had to connect back to metal or the panel somehow. Does wood even conduct? I assumed it didn't, which makes this whole thing seem pointless, but I'm no electrician so maybe I'm missing something about how it works. The wire looks fine otherwise, decent copper, decent connection to the screw itself. Is this some old trick that used to be acceptable, or did the previous owner just have no idea what they were doing? And if it's wrong, where should this thing actually land? Nearest metal box, or all the way back to the panel?


Wood doesn't conduct, so you're right that the connection is doing nothing. A ground wire's whole job is to provide a low-resistance path back to the panel so that if a hot wire touches metal somewhere, the fault current has somewhere to go and the breaker trips fast instead of the metal staying energized. A screw biting into a pine stud gives you basially zero continuity anywhere. Dry wood is an insulator, and even damp framing lumber isn't going to carry fault current in any useful way. My guess is what happened is somebody was splicing or extending the circuit, needed somewhere to stash the ground, and just parked it on the nearest thing with threads. I've pulled apart a few older houses and found similar nonsense, usally from a handyman or a previous owner doing thier own wiring. No electrician I've ever worked with would do that, it's not an old acceptable trick, it's just wrong.

The fix depends on where that wire actualy runs. If it feeds a box or a receptacle somewhere, the ground should land on the ground screw in a metal box, or on the ground terminal of the device, and continue back to the grounding bar in the panel. If the wire is a dead end with no home, the cleanest move is to trace it back and see if you can just cap it off or remove the run entirely, assuming nothing downstream depends on it. As for your tripping problem, I wouldn't assume this is the cause. A floating ground usually won't trip a GFCI on its own, since GFCIs compare hot and neutral current and don't actually care about the ground for tripping. More likely you've got moisture somewhere, a nicked conductor, or a device on the circuit leaking current. Fix the ground situation anyway because it matters for shock protection, then start unplugging things on that circuit one at a time to narrow down the tripping culprit.

Ha, I found something similar in my place years ago, except the ground was wrapped around a nail hammered into the joist. At least a nail touches the box strap sometimes, but still useless. Took me an afternoon to trace it back and land it properly on the receptacle. On the tripping side, if this circuit feeds anything near a exterior wall or a damp basement corner, I'd check the boxes for moisture first. Mine turned out to be water seeping into an outdoor outlet after rain. Dry everything out, reset it, and see if it holds.

Yeah, seconding the guy who traced his back to the joist nail. I had almost the same thing in my kitchen remodel, except the ground was clamped onto a heating duct. Looked metal and official at a glance, but there was no actual path back to the panel, it was just riding on sheetmetal that went nowhere. Pulled it off and landed it on the receptacle ground screw like it should have been all along.

If you trace that wire and it turns out to feed somthing, the panel is the end of the road, not the nearest box. Everything bonds back home eventually.

Before you land that wire anywhere, do a continuity check from that lug back to the ground bar in your panel. I learned this the hard way on my garage circuit, spent an hour re-terminating a ground only to find the other end had never been landed at the panel at all, some previous owner had just coiled it behind the box. Meter showed open circuit the whole way. Took two minutes with a cheap multimeter and a long extension cord for the test lead to figure that out. If yours shows continuity, great, land it on the box screw. If not, you've got a bigger tracing job ahead.

Update: took the continuity suggestion and grabbed my meter. Zero reading from that lug to the nearest receptacle ground, so the run is dead somewhere behind the wall. Then I traced the other end and found it just coiled up inside an old junction box in the attic, never landed on anything. Now I have to decide if it's worth hunting the break or just pulling a fresh ground.