from mains voltages. The insulation of the telephone cable is to protect the user from telecom voltages.

I just said it wasn't 'unsafe' as was implied.
--
fred

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

You may disagree with the regulations. However, they do state that the telecoms wiring must be mains rated if it is to be run in close proximity to mains cables.
Christian.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

As someone else has said, you may disagree with the regulations (and I can understand why - the system is unlikely to be unsafe in practice) but they do state that all cables run together should be insulated for the highest voltage present:
528-01-02 "A band I circuit [e.g. telephone] shall not be contained in the same wiring system as band II [e.g. mains] voltage circuits unless one of the following methods is adopted:
(i) every cable is insulated for the highest voltage present (ii) [discusses multicore cable] (iii) [multicore again] (iv) the cables are insulated for their system voltage and installed in a separate compartment of a cable ducting or trunking system (v) [trays and ladders] (vi) a separate conduit, trunking or ducting system is employed.
[...]
For telecommunication circuits, data transfer circuits and similar, consideration shall be given to electrical interference, both electromagnetic and electrostatic. See BS EN 50081 and BS EN 50082."
Comments in [] by me.
In the OSG this is tabulated in tables 7.3A and 7.3B, section 7.3.3 page 53.
As you have found, there is also a very real risk of interference. Standard mains twin and earth isn't a particularly noisy cable, as equal and opposite currents flow in close proximity, but get *too* close and you'll hear it. (Just thought - if it's a ring circuit it's worth checking that both L and N are continuous right around the ring. If one of them is broken this will lead to unbalanced currents in the loop and will greatly increase the potential for interference). Proper telephone cable should have a twist in each pair which also helps reduce interference, but it isn't perfect.
If you *must* wire this closely, instead of standard telephone cable, choose something like Cat 5 cable which is usually (though not neccessarily always) insulated sufficiently (some brands are marked 1000V) and has a much tighter pair twist.
HTH
Hwyl!
M.
--
Martin Angove: http://www.tridwr.demon.co.uk /
Don't fight technology, live with it: http://www.livtech.co.uk /
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks for the refs Martin.
You are right, I was taking the approach that:

It is not something I would do under any circumstances.
--
fred

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Except that it's what the Wiring Reglulations require...
--
Bob Eager
rde at tavi.co.uk
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thank you those who replied. I have now checked the wiring & found no visible fault. The cable looks correct: solid conductors; colour- coded as on WPP website; pins 2 , 3 , 5 connected in correct colours at both ends; 4 not connected. I cannot tell if the cable is twisted without stripping some and there is no spare length. Massive resistance between conductors ( > 10 megohm). Unplugged master socket, shorted one end, there-and-back resistance about 3 ohm. Sometime I hope to lift a floorboard & see how close it runs to the mains cable...
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 17 Nov 2003 09:39:32 +0000, "M. Damerell"

In the meantime the trick of using a master socket at the extension and connecting to 2 and 5 only may work. Hum is often picked up in the unbalanced 3rd ringing line.
--
Peter Parry.