Perhaps of academic (rather than practical) note unless your cable route & installation method is to plaster in split concentric :-)
Split Concentric does not comply with 526-06-06 in 17th. No RCD required if the cable is run on the surface, in steel trunking/ conduit, or at >50mm depth etc (note BReg AD "A" imposes limits on wall chasing depth). However RCD would be required if you just buried the cable under plaster. RCD protection of a sub-main is no good because you would lose any final circuit downstream RCD discrimination.
SWA does comply with 526-06-06 in 17th. No RCD required if the cable is just buried under plaster, however the size & min bend radius (6*Dia) probably prevents this anyway.
A comment re EFLI testing. Buy a copy of GN3 re testing. The 15ma no-trip EFLI measurement sounds good, but I am not totally convinced by their efficacy. No trip EFLI measurement is indirect via a complex algorithm & tiny test current. If any noise is present during the test the results can suffer poor reproduceability & accuracy, sensitivity analysis of some algorithms is poor. Noise can occur from fluorescent lights (turn off neighbouring CPD), appliances accidentally left plugged in, proximity to the Tx, harmonics etc, even battery level. Eg, Low current EFLI test may produce Zs results varying from 0.9ohm to 1.4ohm which makes validating a circuit design meets Zs limits for a 40A+ Type-B CPD rather ambiguous. Eg, Low current EFLI test results lose accuracy as Zs gets very low (TN-C-S) - an issue if validating say sub-main fuse protection. Meter accuracy can be a flat +/- 10% or a tighter %age with +/- 4-digit variation to consider. I notice calibration certificates are at high Zs levels, such as 0.7-1.0ohms (TN-S supply Ze).
With a low test current the algorithm is highly sensitive, noise may not be rejected but actually magnified. With high current EFLI tests this does not occur, noise that affects a 15ma test is insignificant in a 25A test - but the high current test will trip an RCD.
EFLI testers are live testers. That exposes you to live testing risks (25A test at light fittings will spark at probes). That exposes you to instrument selection (three wire testers can not be N+E joined to test no-neutral light switches without tripping the RCD). Fused test leads are ideally required, which adds to the cost.
EFLI can be determined dead. Regulations permit calculation of Zs - measure R1+R2 via 200ma continuity meter, obtain Ze from supply-type & DNO enquiry (TN-S
0.80ohm, TN-C-S 0.35ohm) or simply measure Ze. PFC obtained from DNO enquiry. Make up your own wander lead or socket adapter (make buy one with 4mm bridge lead as necessary). Some find hook test leads are quick.
Some EFLI meters will measure R1+R2 for you (recent Megger 2-wire testers, LTW325 IIRC) which can save time. Multiple boxes incur multiple calibration charges, single boxes incur less but are a single point of failure.
Just a few comments.