"Kalico" wrote | I remember this being discussed some time ago, but not sure | if we reached a conclusion. | The situation where an RCD is used to protect all circuits | in a consumer unit, rather than just sockets etc in a split- | load arrangement.
I have suggested that a whole-house RCD contravenes the following regs:
130-01-01 Good workmanship and materials shall be used.
130-02-01 All equipment shall be ...installed .. so as to prevent danger as far as is reasonably practicable.
314-01-01 Every installation shall be divided into circuits as necessary to: (i) avoid danger in the event of a fault, and (ii) facilitate safe operation, testing and maintenance.
314-01-02 A separate circuit shall be provided for each part of the installation which needs to be separately controlled for compliance with the Regulations *or otherwise* to prevent danger, so that such circuits remain energised in the event of failure of any other circuit of the installation, and *due account shall be taken of the consequences of the operation of any single protective device*.
from and copyright IEE Wiring Regulations Sixteenth Edition 1991. [* my emphasis *]
The above taken in conjunction with Peter Parry's comments on the number of deaths through falls possibly linked to sudden loss of light on staircases suggests to me that a whole-house RCD is not only in breach of the Regs, but incompetent verging on negligent (unless there are other provisions eg emergency lighting).
You could fit an emergency lighting unit which would help mitigate the risks arising through loss of discrimination, if you decide you need an RCD.
| I have to replace an old Wylex fuse-board that has only 5 circuits:- | 1x30A Ring main (it's only a studio flat) | 1x30A Fan heaters
These would usually be on 15A radials. If its a radial circuit at 30A it should be in 4mm cable not 2.5mm (which is for 30A ring or 20A radial circuits)
| 1x30A Shower
If rewiring, I would suggest provisioning a new circuit at 45A. You could use an RCBO instead of an MCB - most are two-module, but it would save space compared to a 3-module main switch plus 3-module split-load RCD.
| 1x15A Not sure yet as not labelled
As Ed Sirett says, probably immersion heater
| 1x5A lights
| My understanding is that the shower circuit should have an RCD fitted, | although this is not clear from the OSG.
As Ed says.
Owain