This is a 1890s terrace with a TT supply. The incoming mains is protected by a time delay RCD, all other circuits either have RCD protection or are RCBOs.
There are two consumer units:
- Split unit. Non RCD protection, but circuits protected by RCBOs; and RCD protection with circuits protected by MCBs
- Non split unit RCD protection with circuits protected by MCBs (this is where the garage circuit is fed from)
The feed to the garage is through an RCD then a 32A MCB.
The garage has a separate consumer unit with 4 circuits, each of which is protected by an RCBO.
After heavy rain this afternoon, the RCD associated with the garage circuit in the house would trip when the outside lights were energised. However the RCBO in the garage feeding the outside lights didn't trip! Note, I have narrowed the problem down to the outside lights and yesterday (and all night) they worked without any problems.
So is the problem that a combination of leakage around the lights in insufficient to trip the garage RCBO, but in conjunction with potential leakage in the garage - house cable it is enough to trip the RCD associated with the garage circuit?
If so, I have space in a split consumer unit with the RCBOs on a non RCD protected circuit, can I move the garage MCB to the "non RCD" side and still meet the IET Wiring Regulations requirement for an RCD on a TT supply, even though it is a delay RCD?
Regards
Peter