Wiring regs regarding separate isolators

Jun 20, 2019 Last reply: 7 years ago 5 Replies

Whilst swapping my main CU, I am considering having a separate isolator switch so the service fuse will only have to be pulled once. Do the same rules regarding fire suppression apply as to a CU, all metal construction and suitable glands for the tails?



Richard


This isn't a direct answer from the regs but ... Western Power fitted one here in 2017 - it's plastic, but does have two hex screws on each termination.

Henleys are still plastic too.

NT

No. The wording says "consumer units and other similar switchgear assemblies shall be...--- non-combustible."

An isolator is not a consumer unit, and a debate on the IET site concluded a 2 pole isolator on its own is not 'similar switchgear'

Thermosetting, and will not support a flame though.

Sometime soon I'm going to set fire to a leftover BG plastic consumer unit just to see if it supports combustion.

Not sure if I'll be able to get a refund from Screwfix if it does.