Replace FCU with double socket

Mar 18, 2005 1 Replies

In my living room, a spur from the ring main runs to a FCU near the skirting board. From the FCU, cable runs up a chase in the wall to a wall unit display lamp, which is operated via a switch adjacent to the FCU.



I don't use the wall lamp and plan to replace the FCU with a single or double socket, giving me access to extra sockets on that particular wall.



Any problems with doing this?



Thanks Bruce



You will almost certainly be OK.

However there are a few gotchas to do with locations where FCUs are OK but sockets aren't - such as in a bedroom with en-suite shower. No applicable here.

It is unlikely, but there can be unusual arrangements for circuits where this might not be acceptable. If this is a spur in 2.5 T&E off a normal

32A MCB + ring circuit then you should be fine. Unless this would make the circuit so long that the trips times are too excessive, unlikely with an MCB.

You can get a double socket that fits onto a single back box.