How to isolate an SWA termination

I've decided to make both my sheds TT installations, via buried SWA from the house PME. The SWA shield will be connected to earth at the head end so needs to be isolated at the remote end - question is how to do this to avoid having the risk of two earths at different potentials - is there an isolating SWA gland? If not, how do I do it? (Google hasn't helped, yet)

Reply to
mailbin
Loading thread data ...

Could you use a plastic enclosure for the termination instead of a metal one?

Reply to
Mike Clarke

Just take the gland into a plastic box / enclosure[1], and don't add an earth tag. That way the SWA is correctly terminated mechanically, but the armour is isolated electrically.

[1] That can be anything you like, such as a plastic clad CU, and adaptable box, or sometimes for outbuildings an external socket is a handy place. E.g:

formatting link

(a cable then runs through the back of the socket into the building)

These little waterproof adaptable boxes are quite nice also:

formatting link

(TLC Direct have them)

Reply to
John Rumm

I was just wondering how you could actually end up with different earths, if by definition, earth is earth. I'd certainly not expect huge differences in soil between a house and the other end of the wire. could somebody explain why it is not acceptable to have earths at both ends, or is this the classic floating neutral syndrome again. Brian

Reply to
Brian Gaff

I'm terminating into a plastic adaptable box, but it's still going to be possible to touch the outside of the gland if the plastic sheath moves (which it will). I thought I'd seen glands somewhere that have the outside metalwork isolated in some way - maybe I dreamt it.

Reply to
mailbin

That is about as good as you are going to get. There is actually a slight failing in the wiring regs as they currently stand in that you can pull the sheath off the SWA gland without the need for a tool and gain access to the earthed metalwork. Its a fairly minor risk though since your would have to do it at the same time as having an fault on the incoming combined PME earth and neutral.

Reply to
John Rumm

With a PME earth you have the danger that should the suppliers combined neutral and earth be disconnected, then your local neutral and earth will be coupled to line voltage, and typically try to rise toward it.

Not a danger if you are within the equipotential zone of the supply, but could be one if you have access to a "real" and independent earth at the same time.

Reply to
John Rumm

How about putting the whole of termination inside another, bigger box (with the SWA entering through a simple hole (if plastic) or grommet (if metal))? Then the sheath is not accessible without use of a tool. Adds that bit more security; and a bit more profit for the meticulous professional ;)

Reply to
Robin

SWA (PG16) and IP68 rated so will use these for the entry to the adaptable box and make sure the cable is well clipped to the wall before entering the gland.

Reply to
mailbin

Smart arse:-)

Reply to
ARW

I have a vague idea that I have seen heat shrinkable shrouds for SWA glands, but it would have been many years ago.

SteveW

Reply to
Steve Walker

In non critical applications that would be ok as well. Note that the nylon glands don't have anything like the clamping strength you get from a proper SWA gland though.

Reply to
John Rumm

Perhaps a heavy wrap of self amalgamating tape in place of the normal shroud on a standard SWA gland. If applied tightly and thickly that would require tools (a knife) to remove.

Andrew

Reply to
Andrew Mawson

That's what I did when I terminated the SWA in my shed (at the last house).

Reply to
Huge

In my case the cable will be mechanically secured to the wall so I think a stuffing gland will solve the problem, but a self-amalgamating wrap sounds like a good idea if not.

Reply to
mailbin

An easy way is to fit the normal shroud, and then fit another P clip tightly over the narrow end of the shroud and cable, in effect fixing it in position.

Reply to
John Rumm