How many amps...?

I thought the supply into a meter was always on the left?

Reply to
Andy Burns
Loading thread data ...

I'm sure if was a problem it would have been flagged up by now but yes, they do look very poxy don't they?

Makes you wonder if half of the copper on the other side of the meter is a waste of money!

Reply to
R D S

Jack Harry Teesdale has brought this to us :

4mm or maybe 6mm at a guess. I wonder if they are single or double sheathed? I have never seen black double sheathed.
Reply to
Harry Bloomfield, Esq.

From arguments I've had with commercial landlords over the years i've learned that if something is potentially inadequate but historical, it can be left.

Reply to
R D S

It does look odd and a bit skinny. And I bet they would get quite warm if there are highish sustained loads like night storage heating. The 16 mm^2 tails here get warm with only 10 kW of loading. Those black wires look nearer 10 mm^2.

IIRC the DNO is resposible up to the main cutout's output terminals and the MET. The supplier does cutout to meter and the meter. The customer down stream from the meter output terminals and to the MET as required. Trying to get the supplier to pay any attention might be fun and if they can be persuaded to do anything they'll probably sub it out to the DNO...

Reply to
Dave Liquorice

Meter are wired left to right Lin Nin Nout Lout

Nout actually serves no purpose and the neutral to the CU could be direct from the cut out if desired. The neutral is only there to allow the meter to work.

Reply to
ARW

Probably MICC cable. Note the red sleeving on one of the cores.

6mm should do 60A.
Reply to
ARW

Or not.

The cable on the load side might have a different maximum operating temperature to the incoming cable. The bigger the cable the lower the temperature.

Reply to
ARW

That suggests after a closer look that there are 2 CUs and somebody only had red tails on their van,

The two tails on the left are in the neutral bar in the MK block

Reply to
ARW

Well it is upside down and probably an EICR fail.

Reply to
ARW

ARW submitted this idea :

MICC installed by the DNO - I have never seen that.

Reply to
Harry Bloomfield, Esq.

And MICC is often rated at 90 deg operating. (not sure what the meter is rated for though).

At a guess the PVC tails look to be at least 16mm^2 which would make those at least 9mm diameter. Since there are two MICC cables,that suggests a 1H? configuration (i.e. single core with mineral insulation and copper clad sheath). Something like 1H6 (6mm^2 conductor) is only about 6.5mm overall diameter, and that is good for ~50A

Reply to
John Rumm

I've read through this thread with interest. Until two years ago I lived in a tenement flat in Dundee, built c 1890. Obviously gas-lit originally, the electric supply was installed by "the Dundee Electric Co." The single incoming cable was original, about 1.5" diameter. This went to a locked box on the first floor, and power was distributed to the communal lighting and the eight flats in the block I sometimes wondered about the load going through that cable on a cold winter's night, but there was never any trouble in the 20 years I was there.

Reply to
John Armstrong

Input is on the left of most meters...

Reply to
John Rumm

Do neutral tails actually need to be the same rating as the live one anyway ?. Often wondered because the overhead supply to older properties frequently seem to have two uninsulated copper cables where one is noticibly thicker than the other.

Reply to
Andrew

Best not if there is an isolation switch between the cutout and the meter. Just in case anyone followed your suggestion literally.

Reply to
Roger Hayter

Within a single phase installation, then yes generally (unless upstream fusing is adequate to protect the thinner conductor, and the other is just over provisioned)

I would guess that in cases where the overhead supply is three phase and neutral, and they have spread the loads (i.e. properties) reasonably evenly between the phases, they would expect the total neutral current to be noticeably lower than that of the phases. (in an ideal world it would be zero)

Reply to
John Rumm

Trust me, that is the last place an electric co will place an isolation switch.

Reply to
ARW

We are talking about a different country:-)