Hi

I have just two gas appliances in my flat - a cooker and a boiler for the C/H & Hot Water Tank.

When the boiler is running the gas pressure to the cooker drops considerably.

If I have any of the gas hob burners on at full and the boiler starts up the flame reduces to approx half the power.

Could it be that the boiler is drawing too much gas or that the gas pressure is insufficient?

Thanks for any info.

Rob

Reply to
Rob
Loading thread data ...

The boiler should have its own supply directly back top the meter.

_________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download

formatting link
to open account

Reply to
Doctor Evil

Sounds like one of two likely possibilities: Either the dynamic gas pressure (i.e. under load) is falling below spec at the supply from your meter, or the cooker and boiler at some point share a common pipe, and that pipe is undersized.

If you have a manometer you could look to see what happens to the gas pressure at the meter test point when the boiler kicks in (it ought to sustain 21mbar or thereabouts). If it does not then you need to talk to Transco since it is their problem.

If the pressure at the supply end looks ok, then you may need to investigate what is going on with the piping. Full details of how to calculate the sizing can be found here:

formatting link

Reply to
John Rumm

This is not explicitly necessary provided that the pipe system is designed correctly. The applicable British Standard does not require it, and one can look up a design guide based on it at the Copper Development Association.

In this instance, the pipework may be of inadequate size, and *a* solution may be to make a run of pipe from boiler to meter directly. Another is to replace the piece from the tee for the hob and the meter.

Reply to
Andy Hall

... but as a rule of thumb for a boiler up to about 28kW (100,000BTU) the pipework should be 22mm for most of the way to the boiler, up to about 15-20 metres max of pipe run. 15mm pipework causes a _lot_ extra pressure drop.

Reply to
John Stumbles

To get a noticeable effect like you have you will have a significant fault with the supply or pipework.