Earthing (socket & main)

Jun 19, 2005 2 Replies

My house rewire is almost complete and I noticed the electrician hasn't connected an earth to the metal back boxes for the sockets (all the lighting boxes are earthed). He told me the 2 screws holding the sockets on, earth the box, is this acceptable ?



Secondly should he have installed a separate earth bonding connection block ? it looks like he has used the earth terminal in the consumer unit to connect up all the bonding cables, this then connects to the incommer.



Thanks


Yes, unless the back box is exposed.

That's fine if it has the capacity for the 10mm² service bonding conductors.

Yes, for flush back boxes, which are inaccessible to the fingers when the sockets are in place, this is acceptable. For 'metal-clad' wiring accessories, where the box remains acceptable, it is not and a wire connection should be made between the earth terminal of the socket and that of the box.

That's perfectly OK too.