If we've currently got an 8 year old Potterton Combi 100 boiler (which I believe is specc'ed as a 100btu boiler), and which when working supplies the house fine with heat and hot water, is there any reason why I should go any higher than a 30kwh boiler as a replacement?



Looking at the WB Greenstar 30CDi at the moment, but noted that their "calculator" often suggests a 37kwh option instead.



What's the tangible benefit (if there is one) of getting a combi boiler which supplies over-the-top power?



Matt


Better flow rate of hot water. The extra 7kW would give you another 3lpm of hot water, or a 30% reduction in the time taken to run a bath.

As long as the heating side can modulate over a decent range, then there is no real down side to having more power as long as you gas supply has the capacity.

It is also possible that the existing unit is _effectively_ operating at nowhere near the nominal 30kW rating. So that a similarly rated but nnew unit would give a very noticeable improvement.