Can anyone point me to/recommend some wet central heating design software...? thanks
joe
Can anyone point me to/recommend some wet central heating design software...? thanks
joe
ok,i've found one at
ta
joe
That one isn't too bad, Joe, but check the U values very carefully against other sources like the Approved Documents to the Building Regulations.
The Myson program is rather better and I can email you a copy if you drop me an email and can wait until tomorrow - I don't have a fast network connection at present.
These packages only do radiator sizing and generally assume older HW cylinder types with low recovery rates when sizing the boiler. This doesn't matter too much if you are using a modulating boiler.
If you are designing a system from scratch and using a condensing boiler, don't forget to set the flow and return temperatures to 70 and
50 degrees and also to make sure that the program does the correct derating for the lower mean water to air temperature. In effect this means larger radiators but more efficient running over more of the year.One other factor is to check pipe sizing. IIRC, neither program does this. There is a useful paper on pipe sizing at the web site of the Copper Development Association. Once you have the radiator sizes and rough pipe lengths it will allow you to calculate pipe sizes and pump size/setting.
.andy
To email, substitute .nospam with .gl
HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.