I need an additional circuit, but the CU is full. Is it permissible to move a circuit to a new CU and use the freed-up fuse to feed the new CU? (Yes I know I need about Part P)
Cascading Consumer Units.
Jan 12, 2006
3 Replies
Would be a better option in most cases to split the supply via a Henley block to feed both CUs directly, or replace the existing CU with a larger one if space permits.
Just my off-the-cuff opinion!
Yes, but you are obviously limited by the overall rating of the original CU and of the fuseway you use to feed the sub-CU.
What sort of circuits are you wanting to add? It wouldn't be a good way to turn a lighting circuit into three electric showers, for example.
Owain
This is better, but the OP's suggestion is also allowed. Would suggest using a BS1361 cartridge fuse on the way which feeds the second CU, as it will offer better discrimination than daisy-chaining MCB's, where you'll likely find they both trip on short circuit faults.
Join the Discussion
Have something to add? Share your thoughts — no account required.
Didn't find your answer?
Ask the community — no account required