My system is a Worcster combi boiler feeding 5 rads.Four of the rads have got therostatic valves on them .My question is should the valves at the other end of the rads be fuly open. Regards
c/heating
May 29, 2004
2 Replies
The short answer is "No"!
The slightly longer answer is that if you want your rooms to heat up evenly, you need to balance the rads by adjusting the lockshield valves.
There's a lot about this in the DIY FAQs, but briefly: This is best done on a cold day (in winter!) with the TRVs set at max (so as to be fully open). You need to measure the flow and return temperature of each rad - for which a non-contact IR thermometer helps enornously - and turn down the lockshield valves on the rads with the highest return temperatures. The aim is to get the same drop (typically 10 or 11 degC) across each rad. *Then* you can adjust the TRVs to your liking.
Each time the system warms up from cold, the TRVs will initally be fully open, and the correctly set lockshields will ensure that a proportionate amount of heat goes to each room - rather than the rooms heating up one after the other, which otherwise may occur.
thanks set square
Join the Discussion
Have something to add? Share your thoughts — no account required.
Didn't find your answer?
Ask the community — no account required