"John Borman" wrote | After having rewired a lighting circuit using the loop in method, | (Upstairs of which works fine) downstairs seems to trip a MCB. | When all light switches are switched off the MCB is fine but as | soon as one is switched on its trips. ... | Ok I have checked all ceiling roses and all seem fine, but how do | I go about testing the circuit to establish where the short is.
The circuit should have been tested with a megger before being connected ot the mains. Disconnect and make safe the circuit cable at the CU. With all switches closed (ie on) (i.e. you will have to repeat the test for each permutation of two-way switches) and all lamps removed, megger the circuit (i.e. L-N, L-E, N-E all open circuit). This should tell you whether you are looking for an L-N or an L-E fault. N-E would trip an RCD but not MCB unless you have live and neutral reversed.
If it fails the initial meggering, which it should as it's faulty, go to the mid point of the circuit, which should be fairly easy on a radial lighting circuit, break into the circuit by separating the loop-in and loop-out and test each half separately (again repeating for each permutation of two-way switches). Repeating ad infinitum/nauseum will eventually get you down to a single cable.
An alternative and possibly quicker method is to open (i.e. off) all switches and remove all lamps, then megger the switched live (L1) against N and E at each switchplate. E will be present at each switchplate through the circuit protective conductor, but for the N (if it is an L-N fault) you will need a long lead that you can wander round the house with, connected to circuit N at some point
Owain