30amp junction box

is it ok to fit a 30 junction box on a ring circuit with a 32 amp mcb protected by and rcd?

Reply to
fyfie
Loading thread data ...

Yes.

Reply to
Andrew Gabriel

Yup, the cable is only good for 27A at best usually.

Reply to
John Rumm

fyfie laid this down on his screen :

Yes, that is what they were made for. The rating of joint boxes and connectors is only a guide to the sizes of cables which will fit in them, rather than an absolute rating.

Reply to
Harry Bloomfield

When you consider how most electrical junction boxes are constructed the concept of a current rating for them is silly. The terminals merely make a firm mechanical contact between the cables to be joined: but no current flows in the actual terminal. Such terminals should be rated by the size of cable they can join not by the amount of current.