Part 2
210.21-B-2 limits connected load to 80% (even for non-continuous for 2 or more receptacles on a circuit.
==================================== From my notes:
=================================== There were proposals for 2002 (the oldest one I looked at), 2005, 2008 and 2011 to eliminate the table or make it apply only to continuous loads (as the 80% rule is applied elsewhere in the code). All were rejected.
The arguments that are often made to change table 210.21-B-2 to apply only to "continuous" loads are:
1 elsewhere in the NEC the derate to 80% is for "continuous loads"
2 it is a requirement that regulates what happens after the inspector leaves and is unenforceable
3 UL listed equipment (probably only non-continuous) is readily available that violates the rule.
From the comments, it appears that at least one other code panel does not agree. This code panel seems to not play well with others.
The logic displayed seems to be we (NEC) are right they (UL) are wrong. [The other post the argument made at least minimal sense] ==============================
2011 ROP
------------------- delete 210.21-B-2 rejected the ususal argument ======================
2008ROP attempts to delete table 210.21-B-2 - rejected =========================
2005ROP
-------------------------- attempt to get rid of table 210.21-B-2; rejected
*** PORTER: UL agrees with the panel action on this proposal, but not with the panel's statement. 210.23 permits an individual branch circuit to supply any load for which it is rated. For multioutlet branch circuits, use of noncontinuous appliances rated at 100 percent of the branch circuit does not result in a hazard. All branch circuit components, such as the receptacles, branch circuit wiring, and the overcurrent devices, when used for supplying noncontinuous loads, are evaluated for service at 100 percent of their full rating.
--------------------------- negative on a similar proposal PORTER: Section 210.23 permits an individual branch circuit to supply any load for which it is rated. For multioutlet branch circuits, use of noncontinuous appliances rated at 100 percent of the branch circuit does not result in a hazard. All branch circuit components, such as the receptacles, branch circuit wiring, and the overcurrent devices, when used for supplying noncontinuous loads, are evaluated for service at 100 percent of their full rating. =================
2005ROC Comment
*** Questions regarding how this requirement has been applied to products rated more than 12 amps and provided with 15 ampere plugs should be addressed to the responsible listing organization. [In other words, we (NEC) are right and UL is wrong] ======================
2002 ROP
-------------------------- change limits in 210.21-B-2 to continuous; rejected Substantiation: This change is necessary to provide consistency between this section and section 384-16(d), 210-20, 210-19 and other sections requiring the 80 percent rule. Portable appliances (such as microwave units and hair dryers) and relocatable power taps are UL tested for a maximum of 1800 watts on a 15 ampere branch circuit and operate as a non continuous load on these branch circuits without a problem. Panel 20 and Panel 2 have established a Study Task Group to bring some suggestions for a resolution of this issue. UL 498 tests receptacles at 150 percent of their rating so limiting the load on as now required by Table 210-21(b)(2) for noncontinuous load is unnecessary. See also Proposal 20-52 on page 668 of the 98 ROP. Statement by panel: Quote" the substantiation does not justify the reduction in rating to 12 amperes and 16 amperes for appliances rated between 12 and 15 amperes and between 16 and 20 amperes respectively." This Section as revised will make it mandatory for continuous loads only and not for noncontinuous loads. [??? not followed]
substantiation for a similar proposal:
*** A Task Group comprised of members from code-making panel #2 and #20 met on 7/14/99 at Underwriters Laboratories Inc. in Northbrook, IL and developed examples of the diversity of products that utilize 100 percent of the current rating of the plug. These included intermittent duty products such as microwaves, power tools, personal care products, exercise machines, kitchen appliances, and lawn and garden equipment. Evidence of problems stemming from excessive current do not exist with the above products. A review of manufacturers' complaint databases and the U.S. Consumer Product Safety Commission (CPSC) data shows no evidence of problems with cords on these appliances from excessive current draw. ===========================
2010 [ROP?ROC] in favor: The rule is necessary to correlate with the product standards for receptacles. 15A duplex receptacles are evaluated to supply 15A through the individual receptacle contact points. ==========================
2008 [ROP?ROC] The panel continues to maintain that the cord and plug connected load must not exceed the maximum load specified in Table
210.21(B)(2). ===========================
2005 [ROP?ROC] In the past, the panel has made it clear that cord-and-plug-connected devices are expected to be limited to 12 A if supplied by a 15 A attachment plug.