Is it possible/code to pull three #10 and three #8 wires thru a 3/4" steel conduit?
Thanks, Matt
Is it possible/code to pull three #10 and three #8 wires thru a 3/4" steel conduit?
Thanks, Matt
It's probably not physically possible and definitely a code violation. You also have to consider that when you pull multiple conductors through a conduit, you must derate the capacity of the conductors as well
If you have no turns, you could probably get 6 #10 through, but I don't think it'll do you much good.
Looks good to me.
40% fill for 3/4" pipe is 0.2100 sq in.3 #10 THHN = 0.0552 sq in.
3 #8 THHN = 0.1119 sq in.Throw in a bare #10 equip ground = 0.008 sq in. (250-95 table)
TOTAL = 0.1751 sq in. (less than allowable fill)
-------------- Apply the de-rating factor from Note 8:
#10 THHN 40 Amp X 80% = 32 Amps, so 30 Amp protection is suitable.
#8 THHN 55 Amp X 80% = 44 Amps, so 40 Amp protection is suitable.
Jim
Electrically looks OK, but how's he going to get all that around the bends?
It depends on what the insulation is! It is the cross sectional area that matters, as you are not supposed to exceed 40% of the conduit's area.
If all these wires have T90 Nylon insulation, then their cross section area is only 31.8% of the conduit's. If they are TW75, then they are 39.6%, so they would also fit. If they are RWU75 EP, then they are 63.8% of the conduit's fill.
I have a "conduit calculator" available for free at
Good link. Thanks!