Is it possible/code to pull three #10 and three #8 wires thru a 3/4" steel conduit?

Thanks, Matt

Reply to
mistral9999
Loading thread data ...

It's probably not physically possible and definitely a code violation. You also have to consider that when you pull multiple conductors through a conduit, you must derate the capacity of the conductors as well

Reply to
RBM

If you have no turns, you could probably get 6 #10 through, but I don't think it'll do you much good.

Reply to
Nexus7

Looks good to me.

40% fill for 3/4" pipe is 0.2100 sq in.

3 #10 THHN = 0.0552 sq in.

3 #8 THHN = 0.1119 sq in.

Throw in a bare #10 equip ground = 0.008 sq in. (250-95 table)

TOTAL = 0.1751 sq in. (less than allowable fill)

-------------- Apply the de-rating factor from Note 8:

#10 THHN 40 Amp X 80% = 32 Amps, so 30 Amp protection is suitable.

#8 THHN 55 Amp X 80% = 44 Amps, so 40 Amp protection is suitable.

Jim

Reply to
Speedy Jim

Electrically looks OK, but how's he going to get all that around the bends?

Reply to
Nexus7

It depends on what the insulation is! It is the cross sectional area that matters, as you are not supposed to exceed 40% of the conduit's area.

If all these wires have T90 Nylon insulation, then their cross section area is only 31.8% of the conduit's. If they are TW75, then they are 39.6%, so they would also fit. If they are RWU75 EP, then they are 63.8% of the conduit's fill.

I have a "conduit calculator" available for free at

formatting link
that comes with cross-section data for a number of different types of wire.

Reply to
Calvin Henry-Cotnam

Good link. Thanks!